Discuss High Zs reading in the UK Electrical Forum area at ElectriciansForums.net

the second question is regarding the same circuit, they have a fuse spur fed from one of the sockets and then have 6 x double sockets after the fuse spur. The last 3 are out door and the last socket on the ‘radial’ gives a Zs reading of 1.64.
Hi - the max loop impedance for BS1362 fuses can be found in BBB Table 41.2 (d) . This gives 2.3 Ohms for 13A, so 80% is 1.84 Ohms. So looks ok :) .
 
The generic values for the cpc compared to the live conductors is 'live value' x ( live x-section/cpc x-section)

So
2.5/1.5 = 1.667 as above
2.5/1.0 = 2.5 ( with 0.41 gives 1.025)

How are you calculating the Zs as 1.08?

In the ring r1 + r2 should be (R1+R2)/4
This should be added to the Ze value to give the r1 + r2 for all sockets on the ring, but the radial off the ring would not be this value.
It would be this value plus the measured r1 + r2 of the radial portion.
Whatever value you get for the zs on the radial may be above the allowed value for the OCPD feeding the ring, but below the allowed value for the 13A fuse
It says on the inside of my EICR certificate book that 1.08 is the max Zs value allowed on a type B 32 amp MCB. Is that correct?

if the radial off the ring via the spur is higher than 1.08 but less than the allowed value after a 13amp fuse, which value would you write on the test form?
Thanks
 
Is this an old install with 1.0mm cpc?
Roughly for the figures given for the L&N, cable length would calculate to approx 62 metres
the cpc should calculate to approx 0.72 for a 1.5mm and 1.08 for a 1.0mm
you may even get a lower reading on the cpc if there are any parallel earth paths.
I’m not there now but I think it was 2.5/1.5 cable but you have got me thinking now.

there was 2 rings in the house, the other readings were
L .54
N.53
E.91

that looks like what I would expect for 2.5/1.5 cable. The house was built 14/15 years ago
 
It says on the inside of my EICR certificate book that 1.08 is the max Zs value allowed on a type B 32 amp MCB. Is that correct?

if the radial off the ring via the spur is higher than 1.08 but less than the allowed value after a 13amp fuse, which value would you write on the test form?
Thanks
Yes, that would be the correct limit for the ring and the spur up to the fuse.

From the fuse onwards, it isn't protected by the mcb, but by the fuse, so you need to use the appropriate value for that, think it's about 80% of 2.3 ohm, I haven't got my book around.

As for the eic/eicr depends on your software, but I would add an additional line below the rfc entry (no circuit in the cu) detailing the radial off the rfc as a seperate entity but not from the cu mcb

The use of 2.5/1.0 was around the metric versions of the 14th I think, way more than 15 years ago unless there was another phase of use
 
Last edited:
Yes, that would be the correct limit for the ring and the spur up to the fuse.

From the fuse onwards, it isn't protected by the mcb, but by the fuse, so you need to use the appropriate value for that, think it's about 80% of 2.3 ohm, I haven't got my book around.

As for the eic/eicr depends on your software, but I would add an additional line below the rfc entry (no circuit in the cu) detailing the radial off the rfc as a seperate entity but not from the cu mcb

The use of 2.5/1.0 was around the 14th I think, way more than 15 years ago unless there was another phase of use
Thank you for your help.
 
I think I should look again for the loose connection on the CPC, I’m pretty sure the cable is 2.5-1.5.

does the result have to be within 1.67 or is it allowed to be slightly over? I was told 1.67 is what we would expect to see so when would you start to look into it?
 

Reply to High Zs reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
764
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
296
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
940

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock