3) I've never come across an 3kw appliance with a BS1363 plug, but if you have then I'm prepared to be convinced. And some ovens come with a connecting cable, some don't (mostly those requiring 4mm& above).
4) Appendix 15 refers to connecting 2kw appliances to ring final circuits (page 453 BYB). You can connect more than one appliance to one circuit, so long as it is designed correctly.
5) Yes
 
3) I've never come across an 3kw appliance with a BS1363 plug, but if you have then I'm prepared to be convinced.

Not sure if they still do them but screwfix used to sell a 3kW Stanley industrial looking fan heater with a moulded 13A plug on it.
I've replaced a few sockets for a customer who bought a job lot of them.
 

Reply to Hob and oven single supply cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
948
I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with...
Replies
3
Views
2K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock