Currently reading:
honeywell valve fault?

Discuss honeywell valve fault? in the Australia area at ElectriciansForums.net

keniff

-
Reaction score
105
hi guys heres one for yah! went to a call out yesterday as boiler had shut down all timer clocks etc had lost power, so starting from the mcb i started to trace the loss of power, i was stumped i had live feeds going everywhere! then i found i was getting 240v between neutral-earth from all points boiler and controller! any way after finding this i decided to go to the main wiring centre of the heating disconnected all neautrals and found it was the neutral from the hot water motorised valve that was giving 240v any ideas what could have happened to the valve? any one had this before? and i have checked return neutral and ch valve is working fine! :confused:
 
Any disconnected neutral will give 240v when there is a load on and the line is still connected.
I would suggest there is a fault with the return neutral, either open circuit or high resistance not allowing current through.
Turn off the fused spur, isolate the consumer unit and lock off, pull the circuit concerned line from the MCB and place in the associated neutral bar, then measure r1+rn at the fused spur.
If this reading is fine, with the power still off, measure neutral resistance accross the switch of the fused spur.
I personally have had this problem twice, once was a broken neutral between the c/unit and fused spur, once was a dirty switch neutral contact not allowing current through to a water heater.
 
the neutral return seemed to be fine, the other valve (seperate for central heating) is working fine now the hot water valve is disconected, the boiler jumped back to life and now heating controllers are working, got R1+RN continuity from spur back aswell. this is what i find strange?! the hw valve used the same neutral path as all that is still connected and now working! its a hard one to explain.... but im just waiting on new valve hoping this helps?
 
it could be a syncron motor fault if its a three port valve they are very complex
The three port valve is a masterpiece of clever engineering, in that it manages to move to one of three positions using only a cheap non-reversible AC motor, a spring, a couple of micro-switches, a resistor and a diode, and act as a relay for the boiler into the bargain! However, it has obviously required quite a bit of lateral thinking to conjure up, and its operation is thus not easy to understand. Here's how it works.
The spring pulls the valve to position A, while the motor winds it towards position B. If the motor is left continuously powered, it will stall in position B, but if it is fed with DC (produced with the resistor and the diode), then it will stall in any position. Two micro-switches, operating just either side of the 'A+B' point, are used to define this position.
This is the circuit diagram of the innards of the valve:
MidPos1.gif
 

Reply to honeywell valve fault? in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock