Hi


How do you fault find on a zone valve to see if its working.

What are the dead test that can be done on them to prove the micro sw is working. Also just any test really

Not out time long so i think this is a useful thing to know when working on heating systems
 
Assuming its a 2 port, blue and brown drive it open and will spring shut on de energising.
Therefor you should get a resistance reading at brown and blue, the motor winding.

Grey and orange are the micro switch wires. Put your test leads across them and force the valve open manually, quickly and all the way, and as the internal mechanism gets to fully open you will see a zero ohm reading briefly before the mechanism starts to close.
 
Easiest way to check. Power it up if it doesn't move over the motor is foofed. You don't need to swap the whole valve though you can swap the motor very easily and you can pick them up for about 8 quid. Same motor for 2 port and three port so you can really pick them up from anywhere.
 
If you have an iPhone, there is a Honeywell app and it tells you exactly how to fault find everything, I haven't found a better one yet and it's free

can you get this app. for samsung galaxy II?
 
Just fault found a three port valve, not working correctly and have told my plumber that it needs replacing, his reply "are you sure it's not the wiring as its a new valve", why don't plumbers like being told when their gear goes wrong
 
reply "are you sure it's not the wiring as its a new valve", why don't plumbers like being told when their gear goes wrong

Because there is no longer apprentices and then electricians whose experience can be judged by their age,appearance of years.

Nowadays you can be looking at a 40 year old , erm, spark who has less than 5 yrs experience.

Somewhere along the way the public, and plumbers, loose confidence in the dilluted trade.

Boydy
 

Reply to honeywell zone valve in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
768
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
952
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
Hi there, the heating system I am working on has 6 zones and valves for each zone which was working fine with one boiler and one pump. some rads...
Replies
1
Views
1K
1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
602

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock