Discuss Hot tub volt drop in the UK Electrical Forum area at ElectriciansForums.net

robd

-
Arms
Reaction score
339
Hi All,

Been to look at a job with a hot tub 27A load, 30 metre run. Don't do much volt drop calculating but here's what I did, anyone disagree? Thinking 6 mm armoured so:

7.3x27x30/1000=5.91v

max permissible (5% of 230v) 11.5, 5.91 v well within that.

Talk about use it or lose it, took me a lot longer than it should! Thanks for any feedback.
 
Hi All,

Been to look at a job with a hot tub 27A load, 30 metre run. Don't do much volt drop calculating but here's what I did, anyone disagree? Thinking 6 mm armoured so:

7.3x27x30/1000=5.91v

max permissible (5% of 230v) 11.5, 5.91 v well within that.

Talk about use it or lose it, took me a lot longer than it should! Thanks for any feedback.

Looks good to me. :)
 
IF you are thinking about volt drop then you could as an easy check look at the standard circuits in chapter seven of the OSG. For a radial circuit with a 32A breaker on 6mm² T&E cable your maximum length (as limited by volt drop) is 49m, therefore a 30m run would be OK.

However I generally think it is better to do it the way you have done so that you can be sure.
 
Hi All,

Been to look at a job with a hot tub 27A load, 30 metre run. Don't do much volt drop calculating but here's what I did, anyone disagree? Thinking 6 mm armoured so:

7.3x27x30/1000=5.91v

max permissible (5% of 230v) 11.5, 5.91 v well within that.

Talk about use it or lose it, took me a lot longer than it should! Thanks for any feedback.

I would have thought 4mm SWA would be absolutely fine. Volt drop works out to 8.91V so still well within the limits, so as long as Zs is ok then that could save you a little cost.
 
Thanks Richard have an osg, never seen that
Just a quick extract (from green OSG) to demonstrate (also shows max length as 33m for 4mm² T&E confirming Happyhippydad's proposal)
I have also added the notes that explains that Volt drop is the limiting factor where there is no other indication.
Green OSG extract.jpg
 

Reply to Hot tub volt drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all im needing some advice on installing a hot tub, the spec of the hot tub says it requires a 32amp supply, My plan is to run 6mm t+e from a...
Replies
1
Views
719
Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
Replies
3
Views
2K
Hi I've got a question regarding volt drop. When calculating volt drop to a 3 phase distribution board do I use 230v (11.5v) or 400v (20v) The...
Replies
5
Views
2K
Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything. An example...
Replies
1
Views
1K
sorry if I'm dwelling on this but have to supply 230v to a hot tub on PME. load 32amps. separate RCD back at the house, 54 mtrs away. exporting...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock