Discuss SWA cable calculation. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

5544

-
Reaction score
13
sorry if I'm dwelling on this but have to supply 230v to a hot tub on PME.

load 32amps.
separate RCD back at the house, 54 mtrs away.
exporting PME through third core and armoured sheath.
no extraneous conductive parts at the tub.
MCB 40amp type C ZS - 0.57ohms
Cable is going to be clipped direct all the way down.

after calculating volt drop and ZS the only one i can fit is 10mm three core. 6mm will do the V drop but not the Ze.

has anyone got one of these quick apps they can check this.

only asking as this is the first hot tub i have done at this distance.

thanks
 
think OP meant Zs. a better value might be obtained by using a 32A MCB. and why the RCD at supply end?
 
6mm would not comply with the volt drop requirements for a 32A load at 54m circuit length (12.6V).
10mm would at 7.6V

The only way 10mm 3 core, using the armour as an earth as well, would comply (theoretically) with Zs for a C type 40A breaker would be if the Ze was less than 0.23.
 
sorry if I'm dwelling on this but have to supply 230v to a hot tub on PME.

load 32amps.
separate RCD back at the house, 54 mtrs away.
exporting PME through third core and armoured sheath.
no extraneous conductive parts at the tub.
MCB 40amp type C ZS - 0.57ohms
Cable is going to be clipped direct all the way down.

after calculating volt drop and ZS the only one i can fit is 10mm three core. 6mm will do the V drop but not the Ze.

has anyone got one of these quick apps they can check this.

only asking as this is the first hot tub i have done at this distance.

thanks

If you are supplying a Hot Tub with a PME supply i suggest you read your BGB/OSG for additional requirements....
 
If you are supplying a Hot Tub with a PME supply i suggest you read your BGB/OSG for additional requirements....

OSG & BGB give no mention of hot tub installs on PME, only special locations swimming pools and basins has a note regards PME advising the use of an earth rod or grid with a resistance of 20 ohms or less to be connected to the protective bonding. My interpretation of this would be as the OP said there are no extraneous conductive parts it is not required, unless the water within the hot tub is classed as the extraneous conductive part due to connection with submersed heaters etc...

also with an upfront RCD in the form of RCBO or seperate 1 way board the RCD would cover the disconnection times negating the need to have a sufficiently low enough ZS.

regards
 
Then you're interpretation as well as the OP's would be WRONG!! Hot tubs,Jacuzzi's, Swimming Pools supplied from a PME/TNC-S supply will need a supplementary rod being provided. Now tell us why do you think that would be the case??
 
Ok but your statement saying check the OSG/BGB for additional requirements is WRONG as the only mention of a PME supply to swimming pools and basins is if there is extraneous conductive parts which the OP said there is none, I do however agree it's sensible to install such measures or convert to TT to reduce risks associated with PME supplying a swimming pool such as a loss of neutral on the suppliers side and the potential between bonded parts and true earth.
 
Class/treat Jacuzzi, Hot Tub's, Basins as you would swimming pools, where a PME/TNC-S supply is provided, that i would have thought, would be common sense.

The only time i would consider to relax the supplementary earth rod on an external hot tub etc,would be where the hot tub/jacuzzi, is located on a wooden or other insulating floor material for at least 2 or 3 metres all round the tub....
 

Reply to SWA cable calculation. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
397
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
565
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
903
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
488
Upgrading the Hot Tub to a Swim Spa, current power for the hot tub is 6mm 3x core swa to a 40amp mcb and 40amp rotary isolator. Cable is clipped...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock