Hi I've got to go look at a job where the place got flooded about 3 weeks ago and as now all dried out but the sockets in 2 bedrooms and the kitchen are still tripping

just what'd to know where to start fault finding
 
Possibly is no fault just damp still and assumimg they are RCD protected then that is what is tripping them.

IR the circuits and see what the results are, if they are still low then pull the face plates down and dry with an hair dryer, as that's not hot enough to damge cables, if your use a paint scrapper type then be careful.

If you have a junction box hidden somewhere then you may have to improvise somewhat.
 
I would not bother messing around with hair dryers - I would just replace any that had the faintest chance of experiencing water ingress, particularly if they are just standard white ones.
 

Reply to House flood sockets tripping in the Australia area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
834
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock