What about fire alarm, emergency lighting as its 5 stories what are the council saying should be done?

Alarm is straight forward LD2 in communal area and grade A in rooms. It's a standard for the area, it's based on LACORS mixed system, works very well. Emergency lighting they are not specific as long as it complies with BS5266-1:2016
This is the easy bit of the project as it's clearly defined.
 
some of the options I would be looking at would either be a pannel board, Ryefield/bemco or bus bar chamber and individual switch fuses for the distribution...all with a single point of isolation.

I'm starting to lean towards Switch fuses, I'd discounted these as I don't like using Henley blocks at the outset, I tend to think they are an after thought, but if I go Cut-out > Henley > 2 switch fuses each supplying a CU with 25mm SWA I'm covered. I can also use 63A fuse to discriminate between main fuse. This way if I need a second supply in the future I just remove the Henley and go direct to second Switched fuse
 
I'm starting to lean towards Switch fuses, I'd discounted these as I don't like using Henley blocks at the outset, I tend to think they are an after thought, but if I go Cut-out > Henley > 2 switch fuses each supplying a CU with 25mm SWA I'm covered. I can also use 63A fuse to discriminate between main fuse. This way if I need a second supply in the future I just remove the Henley and go direct to second Switched fuse
I wouldn't use Henley blocks...I would use a bus bar chamber.
 

Reply to House of Multiple Occupancy Design in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Pretty new here, so not sure if this question goes into this thread I am not an electrician; however, I plan to integrate IOT devices and...
Replies
8
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
902
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock