Was recently at a job where the dishwasher was getting a voltage through it, checked the spur and the cpc was disconnected. Understand the reason that’s it’s became live is because the cpc was disconnected, what I want to know is why has that caused the dishwasher to have a voltage through it? Should it not go round the live and neutral or am I just being very silly
 
Typically equipment these days have RFI/EMC suppression (pre 1990s = radio frequency interference / post 1996 = electromagnetic compatibility) that are intended to stop switching noise, etc, from circulating in the supply cables and being radiated as if they were antennas.

The usual sort of device has something like 0.1uF for L-N where leakage is unimportant, but around 4.7nF for L-E and N-E to keep the current down to avoid RCDs tripping, etc. Still it results in around 0.35mA for each capacitor of that sort (assuming 230V 50Hz).

So if the CPC is open you will see that sort of current trying to flow given the chance. If is not pleasant, but not dangerous in itself. In some ways that is good as it might let someone know there is a CPC fault before anything goes wrong that would need it for ADS.
 
Everything that is live naturally creates earth leakage even under normal operating conditions. One metre of twin and earth generates a tiny amount of capacitive leakage from line to CPC; 100 metres creates 100 times as much. All the wiring in a house might create a milliamp or two, appliances somewhere between 0.1mA and 3mA each, etc. Normally this is of no account but as soon as the CPC is disconnected, all the tiny leakages downstream of the disconnection point will raise the voltage of the disconnected CPC and everything fed from it, until the current leaking out of the CPC equals the amount leaking in.

What voltage actually appears depends on the potential divider formed by a) the total parallel leakage impedance from line to the disconnected CPC and b) the total parallel leakage impedance from the disconnected CPC to true earth. Anywhere between zero and 230V to true earth is possible, but voltages of 50-150 seem most common on disconnected CPCs. Because the impedances of the leakage paths are high, measuring the voltage with a meter often changes it drastically - making it an example of a so-called 'ghost voltage.'

BTW, 'voltage through it' is not the best choice of terminology. Voltages appear 'between' two points. Currents flow 'through' a conductor.
 

Reply to How does an appliance have a voltage through it?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
771
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
442
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
883
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock