Thanks alot everyone, you guys have been very helpful I really appreciate. I wish my books could explain the way you guys explained.

This makes all sense now RCD does not have impact on the current but effects time exposure and ADS is caused by fault current so it has nothing to do with touch voltage.

I am only wondering like you guys mentioned just because regs says as older installations have no RCD does not make them necessarily unsafe so I understand as ADS is there which is caused by L-E . afcourse along side with main protective bonding etc.

If there is a metal frame light switch and property is old with no RCD and there is some contact between Line conductor and earth or lets say metal work, in the situation how would the disconnection is acheived to prevent electric shock?

MCBS only provide overloading and short circuit protection but would ADS provide protection in the situation mentioned ?

sorry guys I am still in learning stage , maybe I am overthinking about it
 
I am only wondering like you guys mentioned just because regs says as older installations have no RCD does not make them necessarily unsafe so I understand as ADS is there which is caused by L-E . afcourse along side with main protective bonding etc.

If there is a metal frame light switch and property is old with no RCD and there is some contact between Line conductor and earth or lets say metal work, in the situation how would the disconnection is achieved to prevent electric shock?

It gets thrown around a lot that 'the regs aren't retrospective' as if it's the 11th commandment but you need to consider the change of use due to technology too. You will see a lot of properties with only one socket in a room there just wasn't the same amount appliances back then and no electronics. If it's a old lady that still lives like it's the 70s it might still be safe...

In the situation you mention the metal frame would be earthed and the Zs would be low enough to disconnect within 0.4 secs. We only consider one fault so the external conductive part (which I assume isn't in contact with earth or bonded) couldn't become live without two simultaneous faults. A fault outside of the enclosure would be avoided by double insulated wiring which should be adequately protected against mechanical damage.
 
Last edited:
Keep the questions coming.
If there is a metal frame light switch and property is old with no RCD and there is some contact between Line conductor and earth or lets say metal work, in the situation how would the disconnection is acheived to prevent electric shock?
This would cause very high current flow.
Nominal voltage (230) divided by resistance to earth (under 5.82 ohms if installed to regs and it’s a B6 breaker) gives fault current of 39.5 amps.
The graph for a B6 breaker shows this would trip instantaneously.

On a TT system it’s because the resistance to earth will be much higher and there won’t be enough fault current that a different method is needed (an up front RCD)

(Feel free to keep asking questions - but for basic theory John Ward made some very good YouTube videos.)
 
This makes sense now as in TT system we have higher earth resistance so we cannot rely on ADS to occur hence we need time delay 100mA RCD for fault protection and then for higher risk areas 30mA RCD for additional protection.

In TN as you guys explained ADS provides fault protection by disconnecting in 0.4s for final circuits and submain in 0.5s hence RCD is not required as long as we have additional protection in baths such as supplementary bonding or if the sockets are not in a place suspected of feeding outdoor then even without RCD older installations are safe as long as ADS conditions are met.

Sorry the above definitions were just for myself that I understood the concept from you guys properly lol.

Thanks alot everyone, you guys made this so much easier and I really appreciate you guys taking the time and effort to explain.
I wish the videos and books were interactive like you guys made the whole concept so much easy even someone like me understood this.
I tried asking elsewhere on another platform and guys were not helpful.
cheers to you All!
 
It's good practice to install a 100mA type S upfront but not a requirement of bs7671. A single 30mA can serve both fault and additional protection.
You often find older 5 way consumer units with an 30ma RCD main switch providing fault protection and additional protection. (These are the least likely RCD's to ever be tested and I've known quite a few not work)
It's worth adding that for a few reasons it's good if each circuit (or at least group of circuits) have it's own RCD.
a) with the general increase of leaky equipment, if you gather all the leakage of every circuit together this can increase nuisance tripping.
b) with the increase in the amount of DC leakage it's good not to gather it all together in case it blinds the RCD and it fails to operate.
c) It can help if there's a fault to know which instantly know which circuit or group of circuits is the likely culprit. It isn't always this simple but it's a good start.

Most of the time these days every circuit has it's own combined MCB and RCD (RCBO) 30ma protection and this is acceptable for TT installations.
If the consumer unit is a older split load board, with some circuits NOT RCD protected, then the main switch would be an S-Type 100ma RCD on a TT system, or there would be a similar RCD in it's own enclosure before the board.
 
Last edited:
Since when has that been good practice?

I can't see any logic to it other than inviting unnecessary nuisance tripping.
I suppose it each to there own when going over and above spec. Your right with considering nuisance tripping with the increased earth leakage from electronics.
 

Reply to How does Touch voltage work without RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
11K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock