I suppose it each to there own when going over and above spec. Your right with considering nuisance tripping with the increased earth leakage from electronics.

I have no issue with going over and above to improve a situation if it is genuinely well thought out and actually improves a situation. However you have not presented this as a way of going over and above, you presented it as good practice, this implies that the industry as a whole approves of it rather than being your personal opinion.

I still fail to see the point of installing an extra 100mA RCD on a normal TN installation.

A 100mA RCD does not provide additional protection, it will allow a fatal electric shock before it operates so does not provide any back-up to a 30mA RCD. It may however provide a false sense of security for someone who doesn't understand this.

For earth fault protection you already have multiple means of detecting those faults either by MCB and 30mA RCD or 30mA RCBO.

Nuisance tripping will occur with neutral to earth faults because RCBO's (assuming they are used) generally do not disconnect the neutral, so the 100mA RCD will trip as well as the 30mA RCBO. This will defeat the whole object of dividing the installation up across multiple RCDs. Again, in my opinion, it gives a false sense of security whilst having the potential to create a larger problem.
 
Dave so if on TT assuming we are not using RCBOS but splitboard RCD 30mA and for mainswitch 100mA then neutral is no longer an issue so for selectivity time delayed RCD 100mA is a good choice alongside with 30mA RCD ?
Sorry I am just trying to understand why on existing so many TT people are using 100mA if it will cause nuisance tripping and as you mentioned RCBO scenario so I am assuming this is the main reason ?
 
Dave so if on TT assuming we are not using RCBOS but splitboard RCD 30mA and for mainswitch 100mA then neutral is no longer an issue so for selectivity time delayed RCD 100mA is a good choice alongside with 30mA RCD ?
Sorry I am just trying to understand why on existing so many TT people are using 100mA if it will cause nuisance tripping and as you mentioned RCBO scenario so I am assuming this is the main reason ?

Yes if double pole 30mA RCDs are installed, or DP/SPSN RCBO's, then selectivity will occur on either a L-E or N-E fault with an upstream 100mA S type RCD.

If on a TT system you have circuits which do not require additional protection at 30mA then a 100mA time delayed RCD would be used to provide fault protection.
A 100mA time delayed RCD may also be installed to provide protection for the wiring within the DB which is not protected by the RCBO's etc.


With a TT system in some respects you have to choose the lesser of 2 evils as far as the neutral to earth fault problem goes, the tripping problem still exists but the danger of not having a 100mA RCD can outweigh the danger of tripping causing an entire installation to go off.

Also consider how much diverted neutral current there will actually be in a N-E fault on a TT system.

Why you will find a lot of TT systems with a 100mA RCD mainswitch and all RCBO's after it may well be due to them being installed by people who blindly follow a book rather than thinking, or people who just don't bother to keep up to date with their knowledge, or even people who woukd rather listen to gossip and rumours than actually read and understand the rules.
 
Why you will find a lot of TT systems with a 100mA RCD mainswitch and all RCBO's after it may well be due to them being installed by people who blindly follow a book rather than thinking, or people who just don't bother to keep up to date with their knowledge, or even people who woukd rather listen to gossip and rumours than actually read and understand the rules.

Given the fact that RCD failure isn't particularly uncommon, would you consider additional 100mA Type S protection to be unwarranted for TT systems?


Edit: This assumes the installation of DP RCBOs
 
I think it's fair to assume double pole breakers would be used on a new TT installation as it would be needed for isolation, right?
 
Given the fact that RCD failure isn't particularly uncommon, would you consider additional 100mA Type S protection to be unwarranted for TT systems?


Edit: This assumes the installation of DP RCBOs

I don't consider it to be unwarranted on a TT installation.

Personally if I was installing a domestic TT installation I would prefer to install a 100mA S type main switch and SPSN RCBO's for all circuits.
I'd also install the 100mA RCD in a separate insulated enclosure as I feel it is a justifiable departure to do so. I'd probably use the enclosure from a REC2 or similar as they clamp the tails quite nicely and are pretty sturdy.

This is of course personal opinion
 
Why you will find a lot of TT systems with a 100mA RCD mainswitch and all RCBO's after it may well be due to them being installed by people who blindly follow a book rather than thinking, or people who just don't bother to keep up to date with their knowledge, or even people who woukd rather listen to gossip and rumours than actually read and understand the rules.
All agreed. I'm not quite ready to say that are no circumstances with an RCBO board where it makes sense though.
I know you've mentioned single vs double pole RCBO's, but if double pole are used it's a legitimate 2nd chance at fault protection should for whatever reason the downstream device not operate.

It covers some rather extreme scenario's that I accept should not happen in the first place such as a bus bar to case fault or someone slipping with a screwdriver.

Finally several brands of CU have an SPD kit that is fed from an MCB. It's highly unlikely, but a faulty SPD would otherwise have no fault protection. I've not had to consider this one yet, and whether I'd change the MCB for an RCBO etc.

I also prefer an up-front enclosure as whatever the regs say I've never liked metal board + TT.
It used to be such an absolute no-no and very quickly became fine as long as a tails gland and clamp is used.
 

Reply to How does Touch voltage work without RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
11K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock