Discuss How many sockets off a fused spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Wonder how the conclusion to that argument went - he may be still passed out from his winnings!
 
There is no restriction on the number of sockets that can be supplied from a fused spur as the cable cannot be overloaded, however on a practical basis the use of the sockets would need to be limited to a total of 13A total to avoid the fuse blowing all the time so consideration of expected load would be useful.
Agree with what Richard says, check out Appendix 15 of BS 7671, for a pictorial description.
 

Reply to How many sockets off a fused spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I have a switched fuse spur where the cooker hood should plug in to… above the actual cooker. I was wondering if I could swap this out for a...
Replies
7
Views
572
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
397
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
669
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
672

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock