Discuss How to certify a lighting spur off a socket? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
9
I've just finished a small job replacing a bathroom light and adding an extractor fan.

Since it is a very old installation there was no earth to the lighting circuit.

Part of the job was to remove a fan heater that had been supplied by a socket radial.

To overcome the lack of earth situation I've added a switched spur to the end of the socket radial circuit which now supplies the new lights and fan.

So this circuit now has an earth and is RCD protected.

My question is how to I fill in some of the details on the cert? For example, cable sizing is 1.5mm for the lights but 2.5mm for radial, I'm unsure which figure to put in??

Everything is zoned correctly and more than enough tests have been done etc...
 
Suppose there would be harm in providing one each, but the only difference would be the cable size & ocpd. The tests (& results)however, would be for the complete circuit.

Cancel that, just re-read your op. I'd just do the one for the new work, the radial is existing.
 
and full marks to OP for doing it that way some cowboys would have insisted in a lighting rewire.
Agreed, nice to see someone thinking, being conscientious about safety and looking at cost effective best working practice.
To the OP, tel is correct but there is nothing stopping you doing an EICR for the whole circuit if you feel its required. More info is always better (helps out the person following up in the future) and always note down worst case scenario. Potential faults will not discriminate the will often find the weakest link. ;)
 

Reply to How to certify a lighting spur off a socket? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
646
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
701
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock