Hey guys. I am currently studying for 2396 city and guild electrical design exam and I'm stuck on this question. Its asks to determine the residual current rating of an RCD in order to comply with regulation 411.4.204. The circuit in question is a final ring circuit protected by a 20a type C circuit breaker, with a Zs value of 1.69 ohms. Looking at table 41.5, is a 500a RCD required since the Zs value does not exceed 100oms? Thanks for all the help.
 
Understanding what they are giving you will help you understand the answer to the question. Regulation 411.4.204 states where an RCD is used to satisfy the other quoted Regulations this should tell you that without the RCD the the other quoted Regulations are not satisfied, the Zs given and the type C, 20A device should tell you this. You say Table 41.3 gives a maximum value of 1.09 but you have been given 1.69 so what are the possible consequences should a fault occur.
 
Understanding what they are giving you will help you understand the answer to the question. Regulation 411.4.204 states where an RCD is used to satisfy the other quoted Regulations this should tell you that without the RCD the the other quoted Regulations are not satisfied, the Zs given and the type C, 20A device should tell you this. You say Table 41.3 gives a maximum value of 1.09 but you have been given 1.69 so what are the possible consequences should a fault occur.
One consequence would the protective will not operate in the required time (0.4 seconds)
 
One consequence would the protective will not operate in the required time (0.4 seconds)
Essentially yes so the quoted Regulations in 411.2.204 are not satisfied (fault protection not satisfied) but an RCD can be used to satisfy them and this is confirmed in Regulation 411.4.5 now the question is which rating of RCD to use. The question refers to it being a ring final circuit likely to incorporate socket outlets however it does not cite this so this could be deliberate. Would any or all of the RCDs in Table 41.5 satisfy fault protection with a Zs of 1.69.
 
Essentially yes so the quoted Regulations in 411.2.204 are not satisfied (fault protection not satisfied) but an RCD can be used to satisfy them and this is confirmed in Regulation 411.4.5 now the question is which rating of RCD to use. The question refers to it being a ring final circuit likely to incorporate socket outlets however it does not cite this so this could be deliberate. Would any or all of the RCDs in Table 41.5 satisfy fault protection with
If you use the formula stated in 411.5.3 ( Ra x IΔn < 50 ) then none of them comply. 1.69 x 30 = 50.7ohms
 

Reply to How to determine the RCD rating in order to comply with 411.4.204 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Hello, I've recently had an EICR done on my residential let. The property is a 1-bed flat in London on the 8th floor, about 10 to 15 years old...
Replies
54
Views
29K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Hi Everyone, I would like to confirm a question I saw the other day regarding working out the residual current on an RCD The question was...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock