Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and the red socket is a spur.

Screenshot 2023-09-04 002954.png

I need to create a new socket, but the closest socket and the only one I have easy access to is the spur.

Is there any way for me to properly create a socket out of that wiring? I've read somewhere that you shouldn't junction a spur or create a spur of a spur for electrical sockets.

Thanks!
 
Yes. You cannot spur from a spur, but you can introduce a fused connection before the first spur, creating a “fused spur” in which you can have any number of points after the fuse.

Total load of all the spur points is limited to 13A of the fuse.


Does this mean you’ve found the answer to your other thread? Whether it is a ring or a radial?
 
This has bought to mind a quote from the late great Lucien - he once used a phrase that I really liked that cut through all of the complication of normative and informative regs.
He simply said "to be universally recognised as a compliant ring final circuit you shouldn't create a spur from a spur".
That really sums up a complicated situation nicely. As a pedantic detailer I've never liked just saying "Thou shall not" and I've never wanted to try and explain to a non-professional the circumstances under which you can.

To be clear, I'm in agreement that adding a FCU is the best option. I was just in a slightly philosophical mood...

One other thought, is the red socket a single or double?
 

Reply to How to install a junction on ring circuit spur? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
795
Hi! I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's...
Replies
10
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
339
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
675

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock