Discuss How to wire a 240V 3-prong plug? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello!
For this device I have one 240V hot wire and one neutral but the socket is for a 240V 3-prong plug (two 120V-hot wires and one neutral). What can I do to install a 3-prong plug having only one hot wire?
20191031_101432.png

This is the plug
20191030_094935.jpg
 
The receptacle picture shows what I think is the old NEMA 10-50 configuration for 120-0-120 service, once popular for dryers etc. This is now deprecated as it used a single prong for both neutral and earth, hence W (=white, neutral) and the PE symbol, i.e. TN-C with one grounded conductor all the way to the load.

The voltage would be correct with your hot wire connected to one hot prong and the neutral wire connected other hot prong as there is 240V between them, and the device would function, but there might be a safety issue if it does not have adequate switching / fusing for both wires to be hots.
 
The receptacle picture shows what I think is the old NEMA 10-50 configuration for 120-0-120 service, once popular for dryers etc. This is now deprecated as it used a single prong for both neutral and earth, hence W (=white, neutral) and the PE symbol, i.e. TN-C with one grounded conductor all the way to the load.

The voltage would be correct with your hot wire connected to one hot prong and the neutral wire connected other hot prong as there is 240V between them, and the device would function, but there might be a safety issue if it does not have adequate switching / fusing for both wires to be hots.
Lucien, I really appreciate your answer.
Now it is clear how 240V circuits work. I realized I should use the third prong for the ground wire and on the other end fix it to the chasis of the device. And yes, I going to use a two-pole switch to make this device safe.
 

Reply to How to wire a 240V 3-prong plug? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

we just replaced our hot water tank with hot water on demand (natural gas) and still have the old power run for the tank which is 30a 240v. I...
Replies
1
Views
2K
I am wiring a 3 prong 220 plug in a feeder panel with 12/2 wire. Should I hook the ground wire to the ground bus or to the neutral bus? The...
Replies
1
Views
834
Mrs broke the 3 prong plug on the steam cleaner and looking to replace it. Hoover steam cleaner: 120v 60hz 10.0A Replacement prong: 15A-125V...
Replies
1
Views
1K
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
732
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock