Told you last week about the faulty B&Q bollard light in my garden,any way replaced it,then the fun happened.
I’ve installed all the external lighting about 2 years ago,now it’s tripping the rcd.
All cabled in Swa,but not ducted,used 3core 2.5mm.
Fault on live to Earth from conservatory to bollard,it’s a funny one,live to earth on conductors all clear,on the live to Swa sheath there’s a fault.
So it looks like a damaged cable,what would you do.
 
swap the cores over. use the present L for cpc as it's fault to armour, then use what is now cpc conductor for L. don't forget to re-sleeve ends. next question for 10? :mad:
 
Soooooo many happy people on here today.... :tearsofjoy:
I've had a big fry-up so I'm happy as a pig in sh*t....
 
sometimes it's the simple solutions that overcome the hi-tech, by the book, scenarios. once had a brand new 3 core SWA buried and the L conductor suddenly failed open circuit. re-jigged using the black (was E) as L and relied on armour as cpc.
 
Agree,but sometimes it don’t seem right does it,in this instance there’s no chance of renewing cable,without major works,have a good weekend
 
it works, so why worry. time to panic is when the next conductor fails to E.
 
Now the spoiler alert,a damaged cable remains in use :)

upload_2018-2-24_14-20-4.png


:tearsofjoy:
 
Boo hoo - that is 58 pence a day for an addition to your collection. No shoulders to lean on here
GO COMPARE, GO COMPARE!
 
Boo hoo - that is 58 pence a day for an addition to your collection. No shoulders to lean on here
GO COMPARE, GO COMPARE!
Thats for the E30 which I haven't driven in 3 months, I still need to pay for the Subaru as well and maybe another car if I give in to temptation.

I prefer Compare the Meercat as I get a free Oleg toy and 2 4 1 cinema tickets which is a decent saving per year. Wasted on you I bet......... ;o)))))

IMG_0281.JPG
 
I'm outside the house scraping gold off the pavements as I need to pay my car insurance next month, £212 bloody rip off.
£212, bloody peanuts. the way you drive and being a southerner, i'd want £2120 to insure you.:(.oh and just seen the bmw, so double that. :D
 
Thats for the E30 which I haven't driven in 3 months, I still need to pay for the Subaru as well and maybe another car if I give in to temptation.

I prefer Compare the Meercat as I get a free Oleg toy and 2 4 1 cinema tickets which is a decent saving per year. Wasted on you I bet......... ;o)))))

View attachment 40982

Wow.... A southerner AND a BMW driver.... your doomed....
 
Didn't know you lived in the ghetto mate :D
Yep I know its sh!te but us peasants have to survive somehow seeking out a living (I really need to find a job 18 months out was fun, but) next week I pay off the £70k on the mortgage that I had to take out for a business deal.

Then looking at something like this, which I think the other half would freak but f!!cking hey ho you only live once,

Screen Shot 2018-02-24 at 16.09.11.jpg
 

Reply to How unlucky is that,I love Saturday in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for a little advise as I’m not sure what’s happening So I’m looking at moving a two way light switch probably about 100cm away from its...
Replies
12
Views
2K
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
887
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock