Discuss I am allowed to replace the 2.5mm wire from a radial circuit to 4mm and the 16Amp MCB for a 32Amp in the DIY Electrical Advice area at ElectriciansForums.net

vadiro

DIY
Reaction score
2
Could you tell me please if I am allowed in England to replace by myself the 2.5mm cable from a radial circuit to 4mm and the 16Amp MCB it has now for a 32Amp?
 
It's a tough one... if I was being super cautious I would suggest this is not maintenance due to the fact it's a new cable and a new protective device which would imply it's the installation of a new circuit which would require an electrical installation certificate and a building control notification.

Plus, as you're a DIYer... how are you going to test to make sure it's safe?
 
It's a tough one... if I was being super cautious I would suggest this is not maintenance due to the fact it's a new cable and a new protective device which would imply it's the installation of a new circuit which would require an electrical installation certificate and a building control notification.

Plus, as you're a DIYer... how are you going to test to make sure it's safe?
Hi, thanks for the answer. My plan was to use a socket tester which is looking for continuity and polarity.
 
  • Optimistic
Reactions: DPG
Hi, thanks for the answer. My plan was to use a socket tester which is looking for continuity and polarity.
That is a bit like kicking a car tyre to prove the worthiness of the vehicle. It needs testing, certifying and notification to Building Control.
 

Reply to I am allowed to replace the 2.5mm wire from a radial circuit to 4mm and the 16Amp MCB for a 32Amp in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
945
Hi all, DIY'er here looking for a bit of advice so please go easy on me. In my dining room there is an existing single pendant and i would like...
Replies
6
Views
463
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
620
I'm in the process of renovating a house. As I go through room by room I am removing old plaster and as the cables are exposed at this point I...
Replies
14
Views
3K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock