Discuss Adding downlights and keeping the existing pendant - Loop Outs in the DIY Electrical Advice area at ElectriciansForums.net

dp3

-
DIY
Reaction score
0
Hi all, DIY'er here looking for a bit of advice so please go easy on me.

In my dining room there is an existing single pendant and i would like to add 4x downlights. I have looked at the wiring behind the ceiling plate and it is the usual, (Switch Line) (Loop Out x3) (Loop In) the 3x Loop Outs are (Living Room, Extension, Utility Room)

Now i know 3 is a tight squeeze in any light fitment so if i were to add another that would mean 4x Loop Outs, now as far as i can tell this is allowed as the lights are just a radial but please correct me if i am wrong.

My question is so as to accommodate all the existing wires, including the new loop out, could you put them into a maintenance free Junction Box like the Wago 221-4 and then then just have one wire going to your Pendant?


Hope that makes sense.
 
Hi all, DIY'er here looking for a bit of advice so please go easy on me.

In my dining room there is an existing single pendant and i would like to add 4x downlights. I have looked at the wiring behind the ceiling plate and it is the usual, (Switch Line) (Loop Out x3) (Loop In) the 3x Loop Outs are (Living Room, Extension, Utility Room)

Now i know 3 is a tight squeeze in any light fitment so if i were to add another that would mean 4x Loop Outs, now as far as i can tell this is allowed as the lights are just a radial but please correct me if i am wrong.

My question is so as to accommodate all the existing wires, including the new loop out, could you put them into a maintenance free Junction Box like the Wago 221-4 and then then just have one wire going to your Pendant?


Hope that makes sense.
I did that in my bathroom, however the lights were quite large and the maintenance free box near one of the lights so it was easily got to, and by pulling out a light I could access the JB easily. do you intend to put the JB into the floor where it will not be seen or hidden, or have it close to a light or with a plate so it can be accessed? I am surprised no one has replied to you actually, plenty of domestic sparks on here, so here is a bump for you, I hope you get some replies
 
I did that in my bathroom, however the lights were quite large and the maintenance free box near one of the lights so it was easily got to, and by pulling out a light I could access the JB easily. do you intend to put the JB into the floor where it will not be seen or hidden, or have it close to a light or with a plate so it can be accessed? I am surprised no one has replied to you actually, plenty of domestic sparks on here, so here is a bump for you, I hope you get some replies
The JB which will replace the ceiling plate/rose won't be accessible once the ceiling goes back up which is why i was going to use a Maintenance Free one and just have the single twin and cpc cable coming from the JB to the light fitting.

On the other hand, yes there will be an accessible JB above one of the downlights where my Loop In and S/L meet.

Hope that makes sense.
 
As MDJ says, where your existing wiring runs to the pendant, remove it and put it into a maintenance free box instead with a new length of cable to feed the pendant. You can then either piggy back from the pendant to the first downlight or if it makes more sense for cabling run a second new cable from the MF box as a split from the pendant feed. Remember to mark each conductor before you pull it all apart or you won’t have a happy time!
 
As MDJ says, where your existing wiring runs to the pendant, remove it and put it into a maintenance free box instead with a new length of cable to feed the pendant. You can then either piggy back from the pendant to the first downlight or if it makes more sense for cabling run a second new cable from the MF box as a split from the pendant feed. Remember to mark each conductor before you pull it all apart or you won’t have a happy time!
This is exactly what i want to do, but also want to be able to switch the pendant and downlights individually. I just wanted to check that this would be the correct way to do it, from the Maintenance Free JB i will run another cable to the first Downlight and terminate that into JB (Inside this would be my Loop In and Switch Line) this would be the accessible one being above the Downlight.

Thanks for all your replies...
 
This is exactly what i want to do, but also want to be able to switch the pendant and downlights individually. I just wanted to check that this would be the correct way to do it, from the Maintenance Free JB i will run another cable to the first Downlight and terminate that into JB (Inside this would be my Loop In and Switch Line) this would be the accessible one being above the Downlight.

Thanks for all your replies...
In which case you don’t necessarily need to run the full loop out to your downlights, just a ‘hot’ cable feed from the new MF to a second MF for this or even straight to the new switch which would be better if you ever wanted to put a dimmer switch in etc.
 
In which case you don’t necessarily need to run the full loop out to your downlights, just a ‘hot’ cable feed from the new MF to a second MF for this or even straight to the new switch which would be better if you ever wanted to put a dimmer switch in etc.

Thank you, it is always good to hear another suggestion :)
 

Reply to Adding downlights and keeping the existing pendant - Loop Outs in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
450
Hi everyone, We have bought 2 new low-hanging light fittings from Ikea to go side by side above dining room table to replace the single pendant...
Replies
7
Views
854
Hi, I am wanting to add a couple of wall lights to a room that currently has a single ceiling rose. Attached are photos of the one gang switch and...
Replies
15
Views
3K
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
631
I have two downlights in my hall with MR16 bulbs. These are now leds, obviously in the past they were halogens. The fittings are really old and...
Replies
2
Views
898

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock