Hi guys

Now i'd be down for ramming a rod in the ground and calling it a TT unless anyone
could advise differently

not come across these before :)
 
regardless of wether or not you have come accross before, why would you tt it?
because there is no earth provided? if so then you have answered your own question.

if in doubt of earthing arrangement do as durham says and check with dno.
 
It looks like a very old TN-S supply, is there a lead sheathed cable entering the bottom enclosure ? can you not islolate the installation and do a Ze test on the cast iron enclosure, even if its a good reading the DNO should be asked to upgrade the earth connection to the service cable
 
pardon my ignorance, but what the hell is a DNO
 
It looks like a very old TN-S supply, is there a lead sheathed cable entering the bottom enclosure ? can you not islolate the installation and do a Ze test on the cast iron enclosure, even if its a good reading the DNO should be asked to upgrade the earth connection to the service cable

Thanks trebor I will try that.

I spoke to the DNO then jumped into there pass the parcel system rang about 3 other numbers finally to through to the answer machine :) brilliant ?!?!?

but I did get some helpful info from 1 nice lady who said if I rung the emergency number on the day of the fit they'd come and sort the earthing arrangment if necessary.

What I'll probably do is try and get them in put an isolator switch in, not at my expense of course, then they can sort any earthing arrangments at the time if necessary.

normally speaking it would be a cut the seal job but it'll confirm either way what I think about the arrangment.

Thats what I love about this job every corner you turn around theres something new to learn

DNO = Distributon Network Operator
 
now i know what DNO stands for----- Dunno who is responsible, pass the buck
 

Reply to Identification of incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
403
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
358
Short version: does code specify a minimum distance from the panel to the first grounding rod, and if so, what is that distance? Long version...
Replies
1
Views
627
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock