There could be multiple scenarios to explain this, one being a junction box mirroring what you would normally expect to see at a batten holder or ceiling rose.
There could be multiple scenarios to explain this, one being a junction box mirroring what you would normally expect to see at a batten holder or ceiling rose.
Fig 1 shows what is referred to as a radial circuit (sometimes called a 'loop-in' or 'multi-point radial lighting circuit'). which uses junction boxes instead of ceiling roses. You may find this wiring arrangement in older properties.
www.lightwiring.co.uk
Also you could find that connectors are pushed up into the ceiling & they have just brought down a single T&E.
Back in the distant past, domestic lighting circuits used humungeous junction boxes where all of the switches and light fittings joined. Usually there was one hidden under the floor of the landing / for the ground floor lights. The upstairs box was in the loft.
Known as Octopus boxes. They were such fun. Here’s an example
Another type
Back in the distant past, domestic lighting circuits used humungeous junction boxes where all of the switches and light fittings joined. Usually there was one hidden under the floor of the landing / for the ground floor lights. The upstairs box was in the loft.
Back in the distant past, domestic lighting circuits used humungeous junction boxes where all of the switches and light fittings joined. Usually there was one hidden under the floor of the landing / for the ground floor lights. The upstairs box was in the loft.
Most of 20th century up to about mid 1960’s. You’ll notice from the pix above that no earth is provided and that wasn’t introduced for lighting circuits until 1966.
At that point (I guess) an Octopus became unwieldy as you might have a large number of earth wires to common up in one box.
What seems to have happened is that electricians took to the round junction boxes. These were mostly 3-terminal, leaving no place for the earths but the sparks used to just twist the earths together outside the box!
This often meant one box per light. Ceiling rose junction boxes had been around since 1914 and I expect that at around this point, some brainbox expanded it to include the loop in connections that we all know and love.
but back in the day, early 20th c,. relative to my last post. cpc was the lead sheath . can't beat the old ways. bring back steam engines - burn wood and coal. male the stop oil terrorists happy. not to mention scargill.