Discuss I'm considering having 3 phase installed in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
14
Hi

I currently have a 100A single phase supply ( forgive the pun ) & I am considering asking for 3 phases to be installed. I have some workshop equipment that I want to install which are 3 phase and total about 30kW.
My property is fed by 2 cables overground on 7 telegraph type poles. My neighbour has 3 phase to a pole outside his house directly from a transformer. From the pole at my neighbours I am the only other consumer & I use one of the phases. So there are only two of us supplied from the recently upgraded transformer. It looks like I need a further two phases from the neighbours pole ran alongside my existing feed & associated consumer unit.
My questions are:
Do I have to use Western Power for the quotation?
Are there any other companies who can do this work?
Does anyone have experience in this type of installation & a rough guide to a price?
Is there a " standard " domestic 3 phase supply, I seem to remember reading something like 3x60A was below a threshold.
Can I still use economy 7?

Thanks in advance

Greg.
 
only DNO can upgrade your supply. if that's Western power, then you need to get them to quote. mymate recently had 3phase installed. cost £7000, but they had to close a road to get cable from tother side of street.
 
Hi, yes you will have to apply to Western Power to have your supply upgraded, you will be responsible for the upgrade work in your property, new three phase distribution board etc and you will also have to liase with your electricity supplier to get your meter changed.

I do not see any reason why you would not be able to continue with your economy seven but I personally have not seen this on a 3 phase supply, again you will need to enquire with your electricity supplier about this.

Cost is anybody’s guess I’m afraid.
 
only DNO can upgrade your supply. if that's Western power, then you need to get them to quote. mymate recently had 3phase installed. cost £7000, but they had to close a road to get cable from tother side of street.
Thanks, at least mine is in a straight line about 50 metres overground on the same side of the road, so might be close to that price.
 
Apologies in advance for the following question.
Are 3 phases of 60A much more load on the transformer than one phase at 100A

Yes, +60 on each of the other 2 phases but -40 on your phase.
It will have been upgraded (or maybe just replaced like for like) for a reason which won't be for you as they won't have been aware of your plans.
 
Apologies in advance for the following question.
Are 3 phases of 60A much more load on the transformer than one phase at 100A
3 phases @ 60A per phgase equates to approx 180A total load.
 
3 phases @ 60A per phgase equates to approx 180A total load.
Thanks for that, I feared it would be that simple. Many years ago I thought that phases partly cancelled each other out. I must have this confused with something else.
With my neighbour using all 3 phases & my usage doubling the load on one phase then I hoped that reducing the load on my phase by 40A, there would be spare capacity to increase the load on the other 2 phases & possibly balance the transformer load better.
 
Many years ago I thought that phases partly cancelled each other out. I must have this confused with something else.

You're perhaps thinking of;
If the load is perfectly balanced across all 3 phases then there is no Neutral current.
If the phases partly cancelled each other, you'd be getting something for free. :eek: :eek:
 
If it is commercial/business,then the justification is stronger,but if it hobby/passion related,i would spend a fraction of the money,setting up things,so your present supply was sufficient. On what you have stated,this would not be expensive.

This could be time managed,or interlocked,or similar....you would have a spare wedge,to blow on a handsome Harrison,or Jap jig-borer ;)
 
If it is commercial/business,then the justification is stronger,but if it hobby/passion related,i would spend a fraction of the money,setting up things,so your present supply was sufficient. On what you have stated,this would not be expensive.

This could be time managed,or interlocked,or similar....you would have a spare wedge,to blow on a handsome Harrison,or Jap jig-borer ;)
Thanks,
Do you mean 3 phase inverters? I have looked briefly at these a while ago, do they provide a stable output to run cnc machines - do you have any preferred suppliers.
 
Hi.
Modern single phase to three phase inverters are very good.
They can take some setting up with all the parameters avl.
We use them a lot at work with all sorts of machines being run with them.
I have set one up at home to run a meddings pillar drill and it works well.
 
Be aware that if the recently installed transformer to which you refer has been installed under a certain time period [ i think 5 yrs but not 100 % sure, could be 10] then you would be required to pay half the cost of the transformer upgrade, which WPD would then refund to the person who paid for the original upgrade. You would ideally need to make a few discreet enquires before jumping in with both feet.
 
Be aware that if the recently installed transformer to which you refer has been installed under a certain time period [ i think 5 yrs but not 100 % sure, could be 10] then you would be required to pay half the cost of the transformer upgrade, which WPD would then refund to the person who paid for the original upgrade. You would ideally need to make a few discreet enquires before jumping in with both feet.
Thanks for the info, I believe the original transformer was just too old & it's time had come to be naturally replaced. It only serves two properties & neither of us paid for it.
 

Reply to I'm considering having 3 phase installed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
706
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
953
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock