Discuss I'm not sure if the Regs allowed separately bare earths. in the UK Electrical Forum area at ElectriciansForums.net

You lot have gone barking again.

Halt, reality check.

Sham don't do it!

Unless your a registered charity, and determined to cocoon this install for historical purposes, tell your customer where to shove it. Even the National Trust rewire their properties.

TRS, aluminium sheathed cables, bear earths. You lot are nuts. :eek:
 
You lot have gone barking again.

Halt, reality check.

Sham don't do it!

Unless your a registered charity, and determined to cocoon this install for historical purposes, tell your customer where to shove it. Even the National Trust rewire their properties.

TRS, aluminium sheathed cables, bear earths. You lot are nuts. :eek:

Why not with bare earths? I can understand rewiring aluminium cables lead sheathed cables and TRS but as long as the PVC cables that are in use in the installation test ok ie good insulation resistance and the earth is actually from the CU and not a water pipe I don’t really see a problem with the bare earths? Is there some sort of requirement to replace a system that still works and is effective? As I said Regs aren’t retrospective so why would you be saying don’t do it? He is going to upgrade the CU and the bonding so I don’t think it’s any different to connecting to Red and Black PVC? It’s old cable and yeah it’s not to current standards but what is the reason to replace it if it tests out ok and the cable is in generally good condition?
 
Hi - being open, due to my lack of experience with the installation and maintenance of these older systems, I couldn't say with confidence whether the installation satisfied Reg 132.16 or not. So it'd be some level of re-wiring or re-staffing :) .
 
I have not a clue what that means imperial is complete gibberish to me :fearscream:
i therefore beg to educate you:
12 inches = 1 foot
3 foot =1 yard
1760 yards (5280 feet) =1 mile
22 yards= 1 chain
5.5 yards = 1 pole/rod/perch
4 rods= 1 chain
6 feet = 1 fathom
10 chains = 1 furlong
8 furlongs = 1 mile
4840 sq. yards= 1 acre.

what's hard about that?
 
firther info:
2 pints = 1 quart
4 quarts = 1 gallon
2 gallons = 1 peck
9 gallons = 1 firkin.

upload_2018-10-18_10-40-2.jpeg
 
i therefore beg to educate you:
12 inches = 1 foot
3 foot =1 yard
1760 yards (5280 feet) =1 mile
22 yards= 1 chain
5.5 yards = 1 pole/rod/perch
4 rods= 1 chain
6 feet = 1 fathom
10 chains = 1 furlong
8 furlongs = 1 mile
4840 sq. yards= 1 acre.

what's hard about that?
That’s easy enough but what is 7/0.29? And what does that mean in metric also 7/16ths? 3/32nds and so on.

10foot 7inches and 3 wee bits on the tape measure as one guy I used to work with would say:tearsofjoy:
 
Unless I am misreading it Regulation 543.3.201 would deem those cpcs as no longer adequate so I would not be considering a board replacement unless they were rewired.
Ahh I see. But again regs aren’t retrospective so back to the old argument should it be replaced as you wouldn’t replace a Plastic CU with a metal one just because you extended a lighting circuit and you wouldn’t rewire the lighting circuit in the new colours the old colours don’t comply but that doesn’t necessarily mean that they need replacing.

718EDEFD-8EBE-4C12-982E-2D53475AE787.jpeg


4AAE0B98-80AA-40A7-98EC-5E362718B322.jpeg
 
Last edited:
That is for you to decide the level of what you feel is still okay to be left in service, me personally I would be suggesting that should be rewired. You also need to consider was it actually compliant at the time of installation or a later ad hoc addition.
 
That is for you to decide the level of what you feel is still okay to be left in service, me personally I would be suggesting that should be rewired. You also need to consider was it actually compliant at the time of installation or a later ad hoc addition.
I couldn’t agree more if you yourself are in any doubt as to whether or not it ever complied then as its you signing the Cert you have to make the decision
 
I've been on this job to do an inspection before fitting a new RCD OR RCBO board. In most of my career until now the CPC is inside the T+E cable. This property has a separate CPC all through out the building. Only where there has been modifications, modern wiring has been used. If I can prove the ZS is good, is it ok to connect to this system. It's seems to be mainly the lighting that is wired in single sheathed cable which has been ran in conduit. I am hoping if anyone has any information regarding the regs about separate bare earth running through the property. There is a risk of borrowed neutrals if changing to an rcd or rcbo board. The customer does not want a Rewire but wants spots fitted and sockets moving. I have convinced him to change the board, now I am worried about nuisance tripping. However if you could advice about the earth mainly would be a great help. Personally I feel the wiring was good for it's day.

View attachment 44940
I would be giving the customer a quote for a full rewire as well, what a mess, buckle clips, bare earths and double insulated singles, 1950s -60s wiring, must be 60-70 years old now
 
Common cable types explained...

VIR: Vulcanised India Rubber. Single-core unsheathed cables used in conduit. Rubber insulation has an outer fabric layer impregnated with a preservative compound. Tinned copper conductors, stranded in all but the smallest size. Conduit was normally black-enamelled. Domestic installations often used 5/8" or 3/4" slip conduit that was not threaded at joints but clamped by the fittings, a.k.a slip conduit. Continuity required enamel coating to be scraped off and was considered unreliable with cheaper fittings.

TRS: Tough Rubber Sheathed. Construction generally similar to modern T+E, rubber insulated cores with or without a bare CPC, inside a rubber sheath. Usually black, occasionally white. Tinned copper conductors, stranded in all but the smallest size.

Lead sheathed twin: Rubber insulated cores with or without a bare CPC, inside a grey lead metallic sheath that serves as CPC unless a copper CPC is included. Tinned copper conductors, stranded in all but the smallest size. Original work will be jointed in metal junction boxes with continuity clamps that connect the lead sheaths together, rather than bakelite ones.

Imperial sized PVC and PE insulated twin / twin + earth: Construction generally similar to modern T+E but with imperial sized conductors, either tinned or plain copper, stranded in all but the smallest size. Some early plastic-insulated cables used polyethylene insulation which has a smooth, waxy appearance and may be semi-transparent.

Aluminium conductor: Construction generally similar to modern T+E. Conductor soft and brittle regardless of whether copper-clad. Cladding was to improve contact at terminations, plain Al makes poor terminations that tend to go high resistance unless special precautions are taken.

Imperial sizes:
Example: 7/.029 (note position of decimal point carefully)
7 strands of 0.029 inches diameter.
CSA (0.029/2 x 25.4)² x pi x 7 = 3.0mm²

Normal strand diameters: .029, .036, .044, .064, .083
Normal strand counts: 1, 3, 7, 19, 37

Common domestic applications:
Lighting circuits: 1/.044 or 3/.029
Power radials: 3/.036 or 7/.029
Ring finals: 7/.029
Cookers and submains: 7/.044
Tails: 7/.044 or 7/.064

There were other / older systems for specifying cable size, e.g. 3/18 meaning 3 strands of 18SWG. These were not normally used after WW2.
 
Why not with bare earths? I can understand rewiring aluminium cables lead sheathed cables and TRS but as long as the PVC cables that are in use in the installation test ok ie good insulation resistance and the earth is actually from the CU and not a water pipe I don’t really see a problem with the bare earths? Is there some sort of requirement to replace a system that still works and is effective? As I said Regs aren’t retrospective so why would you be saying don’t do it? He is going to upgrade the CU and the bonding so I don’t think it’s any different to connecting to Red and Black PVC? It’s old cable and yeah it’s not to current standards but what is the reason to replace it if it tests out ok and the cable is in generally good condition?

It'll be ok when the house burns down; the new metal CU will be holding up the only remaining wall. :D
 
That is for you to decide the level of what you feel is still okay to be left in service, me personally I would be suggesting that should be rewired. You also need to consider was it actually compliant at the time of installation or a later ad hoc addition.
Have suggested it, he has plastered and decorated it. His even fitted a bar. I feel that in these circumstances that an rcd board would be a good idea. As long as I have a good reason . I can even write it down on the cert. What do you think.
 
When someone opens the board, It has 5 neutrals and 5 live cables and only one earth going out, this can be confusing. It will look look like none of the lighting is earthed.
 

Reply to I'm not sure if the Regs allowed separately bare earths. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
540
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
887
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock