Discuss imersion heater thermostat fault finding in the Central Heating Systems area at ElectriciansForums.net

Reaction score
4
Hi all, hoping someone can offer some knowledge/experience of immersion heater fault finding.

My parents-in-law's imersion heater stopped working, on inspection I found the time switch had failed open. Also the isolation switch neon indicator was dead. The heater itself had a good resistance of 20ohms, good insulation resistance and good continuity back to the time switch via the thermostat control.

I replaced the time switch and isolation switch, tested and called it a job done.

A month later and the fuse has blown in the CU, re-wireable 15A type. Testing of the circuit didn't reveal a fault. I put it down to a very old fuse and replaced it. It's a Memera CU so unfortunately can't get a CB pulg in for it so had to stick with fuse wire.

A week or so later and the circuit has gone again. Not a blown fuse but the live wire at the CU to the immersion heater had melted, and unfortunately the wire terminal in the fuse slot had fused making that slot unusable.
Tests of the heating element & insulation resistance were all fine. So now I'd put this down to a damaged wire after the initial fuse blow and then a failure of the now weakened wire.
At this point I've left that circuit disconnected, no hot water for the in-laws, as it needs further work and investigation.

I should add that checking the timer (mechanical type) I can tell that the circuit has failed after several hours each time I've had to investigate. So it's not switching into a dead short.

Questions:
1) I have to revisit my assumption of an old fuse causing the blown fuse and damaged wire causing the second failure. A genuine overcurrent is more likely. So why can't I find an insulation failure or shorted heating element?
2) I've not been able to test the thermostat turns off as I've a cold tank and a minimum temperature of 40 on the thermostat. Could the fault be that the thermostat is stuck on and the fuse (and the wire) failed after hours of full load current, where as it would usually only be an hour max until it reaches temperature.
3) the damaged slot in the CU, and the age of the CU make reinstating the circuit as it was impossible. The preferred option is to completely replace the CU and bring it up to regs. However they are in the middle of selling the house and the new owners (if they have any common sense) will rewire the lot. So in the immediate term my suggestion is to put the immersion heater on a FCU from the ring main. Do you think that's sensible?

Thanks for reading and for your help.
 
Hi Andrew, welcome to the forum. I can't read your profile, so we have no idea of your competency. I think despite your bravest efforts, you have thus far failed to resolve this fault, and it seems you now have some damaged cabling & terminals/connections that will need replacing.

If you are not a competent electrician, I would recommend your parents-in-law employ one, no offence meant to yourself. This forum does not allow step by step guides to DIY'ers, and as it seems there might be several things wrong with this install, it would be wrong to suggests fault finding from afar, which may leave other faults in situ without rectification.
 
No offense taken. I've done my electrical inspection and test qualification, 2391-52, so am considered competent. Although my day job is as an electrical design engineer for aerospace so I do have limited experience on domestic wiring.
When I say I've tested the circuit, I mean I've tested to the procedure set out in 2391 with a multi function tester. As I say I've not been able to see any fault with the immersion.
When it was just a time switch that looked faulty it was an easy fix but for changing the CU or changing the circuit to a FCU I would get an electrician in, mainly as I'm not Part P registered.

Thanks for the input telectrix, any idea how to diagnose that type of intermittent fault. Or is it just a case of change the heater and see if the problem goes.

Just to say again, I will get an electrician in now but just wanted to learn if you would have approached this differently. And if you think a FCU will be ok? As the in-laws are selling the house I'd prefer not to install a new CU at this stage if possible.
 
Hi - it certainly seems that an overload current has been carried in the circuit and this has now damaged some components. I agree with the previous posts, you'll need help to fix this one.
 
Is it me, do I need to go to specsavers, but I have OP #4 (as an alert)coming on-line after tel's #7, yet the order of posting is shown as above? Very strange, seen it before on other threads.

Back on topic, I would agree as tel's suggested, is the original fault. What are the IR readings when testing the element (disconnected), live to earth?
 
Is it me, do I need to go to specsavers, but I have OP #4 (as an alert)coming on-line after tel's #7, yet the order of posting is shown as above?
This could be because as a new member my posts have to be approved by a moderator first before they appear publicly.

IR readings @500V, element (isolated at DP isolation switch) to tank & PE >5GOhms. isolation switch supply L-N >5GOhms, isolation switch supply L-PE >5GOhms.

So sounds like i need to replace the immersion element as well as fix the connection to the CU.

Would a normal electrician be able to fit a new immersion heater or do i need a plumber as well now?

Can any one see an issue with using a FCU to connected the immersion circuit to the ring main, thus saving a new CU?
 
Are you sure of your Gohm unit? Not farmliar with that myself.

If the element is pants, I would use a plumber to replace it myself. Some others on here would do themselves. Putting immersion on an RFC is not a great idea, but as a short term measure it might be ok
 
^^ what do you mean by normal electrician?

Are you not a spark?
I've passed my electrical inspection and test BS2391-52. But i don't work as an electrician, and i'm not Part P registered. In my day job i design power electronics for the aerospace sector - I've done the BS2391 qualification so we have someone on site that can inspect and test our test equipment installations.

Are you sure of your Gohm unit? Not farmliar with that myself.
result was 5000 Mega Ohm, which is 5 Giga Ohms (GOhm).

If the element is pants, I would use a plumber to replace it myself.
Thanks, i thought that would be the answer. I'd prefer to be sure the element is faulty first but so far no one has been able to suggest a method to test the thermostat.
 
Ah looking into it, it seems you can replace the thermostat without replacing the whole heater assembly.

So now i need to be sure its the thermostat that is faulty (not turning off once temp has been reached) as i suspect.
Or if the element has an intermittent fault that only appears when its been heated.

Considering the thermal damage to the circuit wires in the CU, and the fact that the circuit has failed only after several hours of being active. ( time switch shows the element had been on for hours before the circuit failed). I'm leaning toward the thermostat being stuck on and so the circuit is conducting 11A continuously for hours which gives a longer term thermal overload.
 
result was 5000 Mega Ohm, which is 5 Giga Ohms (GOhm).

Thanks, i thought that would be the answer. I'd prefer to be sure the element is faulty first but so far no one has been able to suggest a method to test the thermostat.

A reading of 5Mohms, would be quite an acceptable reading IMO, but as tel says heating of the element can affect the insulation of the element.

A modern thermostat will have an overheat stat, but that's only to prevent the water overheating and circulating into the cold water tank, its not going to cause the fuse to go. As Westward said, and as I did before, you need to rectify these faults. Not suggesting domestic circuits are more complicated than aerospace circuitry, but its horses for courses; I still would recommend getting a competent sparks to investigate.
 
There seems to be a bit of a plumbers approach to fault finding going on here, just replacing parts until it starts working again without a real logical process of fault finding.

If the thermostat has failed closed and the circuit remains live for a couple of hours then someone would have noticed the water boiling or the overheat cutout (if fitted) will have operated.
If the thermostat has failed open a simple continuity test will identify it.

As far as I can see only the supply cableing has been IR tested and not the actual heater element so far?

The cable melting at the terminal in the CU suggests a possible poor connection there.
 
If the thermostat has failed closed and the circuit remains live for a couple of hours then someone would have noticed the water boiling or the overheat cutout (if fitted) will have operated.
If the thermostat has failed open a simple continuity test will identify it.

Continuity of thermostat has been checked and is closed as expected with a cold tank so i know it hasn't failed open.

Your might be right that someone would have noticed the water boiling if it had failed closed- although my parents-in-law are old and have medical issues so i wouldn't bet on it. (hence them currently selling the house to move into sheltered accommodation). This thermostat doesn't have a cutout

As far as I can see only the supply cableing has been IR tested and not the actual heater element so far?
I tested between heating element line connections and PE, this gave a high insulation resistance of 5 GOhms. I did actually state this in post #9

just replacing parts until it starts working again

I think that is a bit unfair.
On the first time round I identified a failed mechanical timer and no other faults: continuity, IR and element resistance all good. The mechanical timer is at least 30 years old. So i think it was fair to consider it a failed part and simply replace it.

The second time around a fuse had blown - again all tests came back OK, no obvious cause of the blown fuse. All tests, continuity, IR & element checked out. No visible damage other than the blown fuse. Again with nothing to go on I think it was fair to replace a fuse, consider it was perhaps due to a 30 year old fuse being disturbed when the circuit was first examined.

On the third time round, no blown fuse and no power to immersion heater. clearly continuity issues which on investigation was found to be broken wires due to thermal overload in the CU. Clearly there is an unidentified fault and that's how I've left it.

I'd like to hear what you would have done differently?
 

Reply to imersion heater thermostat fault finding in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
865
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
867
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
228
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
838
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock