A kit is good. A kit with explanation and discussion even better!
IMHO offering a kits with explanations support an open development so long as copyright is not claimed. Others can then learn from the kit.
Better still sell the AC side properly built and boxed, that would leave others able to develop the digital side.
I would be keen for example on a AC proportional control module rated to 3KW and accepting, say, 0 to 5V demand with the demand appropriately buffered and isolated within the module.
On practical level I find it hard to see where a company would find the ROI to support development, testing and qualification as there are
either patents preventing us and/or our discussions have now limited the field for new patents (well done all!).
Commerialisation would be hard as we are after all talking about a very simple design, one that would be easy to copy,
easy to add new feature and then claim as original design. Those pursuing the commercial route would need a patent or some magic other
device property (cost, features, company reputation etc.) in order to head off alternatives. The fact that several here have developed
their own system would tend to make this case. At a certain market size some of those playing catch up will have surface mount and will therefore trash all for cost and reliability whilst also having a company name which can be trusted.

There was some earlier discussion on patents.
The Emma patent LOAD MANAGEMENT CONTROLLER - Cooper, Timothy Patrick would seem to cover all the devices which we have discussed. Perhaps
I am wrong, I would be grateful for a second reading and some discussion. If I am wrong and there was a gap in the patent
then have we now prevented new patents through our discussion?
Personally I find it quite hard to accept the Emma patent. I am sure that I have read about similar home energy management systems in the past. I have in the past designed control systems which monitor supply and control output currents to match available power (DC only). Where is the intellectual effort/novelty in saying finite input requires managed output control?
Sunny Boy's home manager SUNNY HOME MANAGER.*SMA Solar Technology AG capabilities would seem to overlap the Emma patent, wonder what that's all about.
To open the field to both competing commercial and, to a lesser extent, free open collaboration then we should post any references to articles which
pre-date and therefore may invalidate the Emma patent.
In my view the Emma patent is simply too far reaching and may stifle the development of energy saving devices, whilst only providing an expensive solution.
That cannot be good for the planet.

If Emma were innovative to say £200 or so (the bits cannot cost more than £50 in volume) then I would be more inclined to believe some effort which justified protection and commercial return.
 
Last edited by a moderator:
Hi
I have obtained the pdf versions of the EMMA patent. If any body wants a read send me a private message with an email and I will forward it on. Tell me what you think. I personally dont want to get into any thing on the legal battle side as I cant aford to go head to head via laywers. :-(
 
Hi
Tell me what you think. I personally dont want to get into any thing on the legal battle side as I cant aford to go head to head via laywers. :-(
I don't think we need to worry about lawyers right now.
Noone is going to take a home hobbyist on. I brought up the EMMA patent to settle the confidential design/commerical debate.
I would be keen to see the patent disappear though.
I am pretty sure that power control similar to the EMMA has been discussed before the EMMA patent. I may be wrong.
If anyone finds an article published before the EMMA patent then post. Thats pretty much all we have to do.
If we find the evidence then we will open up competition to those who know how, competition giving rise to improvements, hopefully cost savings, more improvements etc, etc. Once the systems are reasonably priced we can all just buy one rather than risk a home fire (Mr EMMA thats a market gap hint).
I am especially miffed about the EMMA patent as I had the same idea round the same time but through a number of reasons (thought it had been discussed before, was told that meters ran backwards etc) and a medical condition (bone idle) left it alone. Secondly the EMMA cost is really high.
I think that SB home system overlaps the EMMA patent which if so is interesting. SB seem switched on and seem to have a green home game plan. They have had digital interfaces in their inverters (bluetooth now) for a while. I think that may reveal a plan which may predate EMMA. Hoping anyway.
 
I don't think we need to worry about lawyers right now.
Noone is going to take a home hobbyist on. I brought up the EMMA patent to settle the confidential design/commerical debate.
I would be keen to see the patent disappear though.
I am pretty sure that power control similar to the EMMA has been discussed before the EMMA patent. I may be wrong.
If anyone finds an article published before the EMMA patent then post. Thats pretty much all we have to do.
If we find the evidence then we will open up competition to those who know how, competition giving rise to improvements, hopefully cost savings, more improvements etc, etc. Once the systems are reasonably priced we can all just buy one rather than risk a home fire (Mr EMMA thats a market gap hint).
I am especially miffed about the EMMA patent as I had the same idea round the same time but through a number of reasons (thought it had been discussed before, was told that meters ran backwards etc) and a medical condition (bone idle) left it alone. Secondly the EMMA cost is really high.
I think that SB home system overlaps the EMMA patent which if so is interesting. SB seem switched on and seem to have a green home game plan. They have had digital interfaces in their inverters (bluetooth now) for a while. I think that may reveal a plan which may predate EMMA. Hoping anyway.



The EMMA people did a mailer via LinkedIn contatcs a few months back. I first contacted them last year so they must have picked it up from that. When I spoke to them this time, they said Mk II version is due out soon - I thinkk they said this summer but don't quote me on that - and it addressed the high cost issue.

Still waiting. I am absolutely convinced this is the thing to do with spare power but only at a reasonable cost. i.e. hundreds, not thousands. Will be very interested to see what SMA quote for their new peice of kit
 
Actually, it really is just that despite the talk on the thread. EMMA is a switching device that allows PV surplus power to be directed to an immersion. Alternative devices are scarce and knowledge of them would be welcomed by all looking at this thread.
 
Hi TonyL,
Not sure that I understand your post.
Are you saying that you originally had the idea for dumping spare PV power into heating?
Did you communicate via email?
The cost should be low hundreds. There is nothing complicated in this design, all the technology (as I would do it) is well established, its just a small control system really.
The component costs would be well under £100. The rest goes on development, marketing etc. A system could easily be developed & qualified in under 3 or 4 months, say £50,000 development cost. Plan to sell 500 so add another £100 to recover development. Add another £50 for support manuals etc. I just don't see the price tag.
Unfortunately the SMA system seems likely to cost £1000 or so.
Again I don't see where the costs come from but the system may be better featured.
 
The EMMA people did a mailer via LinkedIn contatcs a few months back. I first contacted them last year so they must have picked it up from that. When I spoke to them this time, they said Mk II version is due out soon - I thinkk they said this summer but don't quote me on that - and it addressed the high cost issue.

...... at a reasonable cost. i.e. hundreds, not thousands.

Far as I can tell they are promising a new range called Cascade in Sept but it is for large installations so not addresing the cost issue for you and I. My unit is less than hundreds.

The SMA kit will only switch loads on an off so does not do close load matching.
 
Noone is going to take a home hobbyist on.
Not only because it wouldn't be worth it but because there would be no legal grounds to do so. However, if anyone is using intellectual property covered by the patent to make money, they may well do, and I presume that is one reason why people here selling kits or complete units are being cagey about what their systems consist of.

As for home fires, well of course there is a risk, but if you are competent at electronics the risk is very small: if the relay sticks closed or the triac fails short circuit, it will merely supply full power to the immersion heater, which will switch itself off with its existing thermostat.
 
I'm an idiot (in the Greek sense of not being one of you guys who understand electrics) but I do have a solar pv system and a conventional 3kW immersion heater, and I recognise that there is an obvious need for a system to store surplus electical energy as hot water. So there's an obvious need for some sort of switching/power reduction device of the sort you are collectively developing and discussing, and there's no reason why it should be particularly expensive, since (forgive the idiot language) it's really just an intelligent switch (I could do it myself if I sat in the airing cupboard all day with my Sunny Beam, waiting to turn on the immersion heater at those magic moments when the generation reached 3kW. Of course, it would be better if I could divert just the available surplus generation... but even I can see that this isn't an insuperable problem....). What is clear to an outsider is that there will be a sizeble market for this sort of product in, say, five years' time; that it's understandable that people would want to protect the value of their ideas; and that it's laudible that people should want to benefit us all by producing a collective, open source solution. Probably the commercial model will win; but it doesn't have to be patented. Volvo developed the 3-point seat belt, and deliberately didn't patent it. It's a commercially viable idea nevertheless. Lots of people make them. Presumably they all make a living from them. I hope that between you you'll produce a cheap, safe, viable and marketable solution soon, and that everyone will benefit. I'm impressed that you are trying...
 
Not only because it wouldn't be worth it but because there would be no legal grounds to do so.
I think that the EMMA patent covers use of phase controllers.
inie meanie has downloaded the PDFs and I have posted links.
I would be interested in your and other's views as I am new to the language of patents i.e. do these patents cover a specific design or do the patents cover all designs, used in this PV context, which embody a phase controller?
Again I find it hard to understand how a patent may restrict designs which use well understood components, its would be like saying that a resistor were part of the patent claim and that therefore all solutions which use resistors are covered by the patent. Daft.
Anyway would be interested in views as the systems on offer are very expensive and competition (open or commercial) would be best.
 
Last edited by a moderator:
I think that the EMMA patent covers use of phase controllers.
inie meanie has downloaded the PDFs and I have posted links.
I would be interested in your and other's views as I am new to the language of patents i.e. do these patents cover a specific design or do the patents cover all designs, used in this PV context, which embody a phase controller?
Again I find it hard to understand how a patent may restrict designs which use well understood components, its would be like saying that a resistor were part of the patent claim and that therefore all solutions which use resistors are covered by the patent. Daft.
Anyway would be interested in views as the systems on offer are very expensive and competition (open or commercial) would be best.

Hi Bradburts
Basically the Patent covers the principal of a household load management system that allows the spare electricity to be dumped into another house hold load. Ie. Immersion heater. I am not sure if this patent has actually been granted or is still in the applied format. If it still is in the applied state then there probably isn't too much chance of it being granted as so many other people are all working on other types of load management. It might be a bit of a scare tacktic to halt the competition.
 
Hi,
U sure? M
y understanding is that the EMMA patent was registered 2 years or more ago. Others may work in this area now but as I understand it if the original first published 'design' is the patent then EMMA people have the rights.
I would be interested & very pleased to be shown to be wrong.

I have no experience of patents but as I understand it the patent falls if others have discussed similar designs before.
Please post if any such designs found.
I am sure that Star Trec have many episodes dealing with energy & load management (the crystals are always failing). Wonder if some solar powered space station attacked by klingons used load control. I'm off to check.
I'm working! I will tell the wife as I go through the last 40 years of scifi.
 
I don't know much about electricity - I assume it's like plumbing but with smaller holes for the electricity to pour through - but it has just occurred to me that I do have an old friend who is an intellectul property lawyer. I'll try to get him to look at this thread and report back. (This may take some time...keep on inventing solutions...)
OG
 
That would be great.
I have been researching some more & the following seems relevant:
1) (1974) Load management detailed in U.S. Patents 4,241,237 and 4,455,453 and Canadian Patent 1,155,243 (Apparatus and Method for Remote Sensor Monitoring, Metering and Control)
2) 'Smart grid' as used in 2005 "Toward A Smart Grid", authored by S. Massoud Amin and Bruce F. Wollenberg appeared in the September/October issue of IEEE P&E Magazine (Vol. 3, No.5, pgs 34–41)
Seems to me that the EMMA system is a form of 'economic demand response' that is to say it costs you nothing to use the PV and costs you to use the grid. Selecting one supply or the other is therefore an economic demand response.
I was very happy to find that load managment has been discussed since 1974. I think therefore that there is nothing to worry us in the patent, just the difference between macro and micro grids.
I also found reference to office lighting systems which dimmed as a response to grid load.
http://www.lrc.rpi.edu/resources/newsroom/pdf/2004/LoadShed.pdf
I suppose therefore/also that I/we could offer systems which dimmed lights (say a 3KW system for those with big houses) when PV output was low & before we start to tax our fragile grid.
The light is not an energy store (as discussed by EMMA) and light dimming has been done before, see link above.
Of course I would be powerless to stop someone fitting the dimming device to an immersion heater..........


Think inie meanie was right. Would be great to have a proffessional's view though!
 
The difference between patent theory and practice is that even if a patent is ultimately invalid, if the company holding it decides to prosecute you because you are selling a product that infringes it, you could spend a large amount of money defending yourself in court.
 
The difference between patent theory and practice is that even if a patent is ultimately invalid, if the company holding it decides to prosecute you because you are selling a product that infringes it, you could spend a large amount of money defending yourself in court.
Agreed.
I hope however that as the prosecuting company would need to spend money they would not, especially if there is a lot of 'holes' on clear display!
I will post as many 'holes' as I can find and hope that the wiser explain their validity.
I hope that somewhere along the line someone will think that the route is open for their own system to go to market but at a much lower cost.

BTW, old growser,
You're right, the control systems being discussed are quite simple. A microcontroller monitors both PV generation and home use using a pair of current transformers. The microcontroller then controls the amount of power going to the immersion heater using a phase controller. A phase controller is a posh name for the circuit in your light switch dimmer, it works by switching the AC on some way into each AC wave cycle and therefore limits the amount of power being transmitted in each cycle.
Some are using simply relays which have the advantage of being even simplier to design. The problem with a relay solution is that a relay cannot be switched on/off within the AC wave and therefore a relay will clock any meter at the relay's load's rating, typically 3KW for an immersion. The relay's PV generation trigger point must therefore be much higher than the phase control system. Using a lower watt immersion heater lowers this threshold but at cost and hastle. Adding a diode in series would reduce the 3KW to 1.5KW. Your trigger point PV generation would then be, say, 2KW, 1.5KW for the immersion and 0.5KW for the home.
You're right you could be the control system by sitting in your airing cupboard, with unemployment and energy prices going the way they are you may be able to employ someone to do this, start a company and see if you can get an intern! Technically you would be open to prosecution (if you think that the patent is valid) though as 'a switch' is described in the patent, the patent also covers Thyristors which suggests use of a phase controller (which is just a more advanced switch synchronised to the AC waveform).
Most in this forum (it would seem independently arrived at design that) think that a phase controller would be the best way to go. By far the most effective system is a phase controller as it allows you to control power dumping with a high level of resolution thus sucking up all the excess power rather than having to reach a generation threshold related to the immersion heater's power rating.
 
Last edited by a moderator:
Phase controllers (despite my intention to use one) have two disadvantages:

- they generate heat
- they generate electromagnetic interference, which to suppress properly (i.e. to comply with regulations for a commerical product) is bulky and expensive for this sort of current

Actually, aren't there regulations stipulating that power factor correction is needed on any appliance drawing over a certain amount? This would add even more to the cost. And the use of a simple diode to reduce power consumption by half would also need power factor correction in this case.

There's no reason why an immersion heater controller should need to sense both house and PV current; if it gets a sniff of the voltage waveform you can tell which way the current is flowing in a meter tail so one current transformer is all you need.
 
Hi suntrap,
Having just one CT would be a nice simplification.
Forgive my ignorance but how would you sense the direction by looking at the voltage waveform?
Your right power factor will drop. I recently scanned the low voltage regulations looking at CE marking but did not see anything about power factors. Do you have a link?
I agree heat could be an issue. I gather that Rds values can be really very low these days though.
RF is always fun. Best bet with RF is to sacrifice a cat under the full moon, that’s what the RF engineers I know do, I'm sure.
What do you think the EMC problems would be?
I am not sure that there would be a major EMC problem though.
I have read a few application notes and have not seen any mention of EMC, the application notes are very detailed as well (enough for a softee like me to understand!).
Also I don't remember the EMI rules forming a distinction between continuous emissions and discrete and a relay switched on or off would chatter albeit for a short duration.
A phase controller would pulse giving you a step at 50Hz for sure.
13Amps is a lot to switch but how many multiples before we get to a regulated band?
Have you done any calculations? Is the simple on/off at 50Hz circuit in the face of the standards or marginal?
 
Last edited by a moderator:
New posts

Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
442
The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
391
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock