Hi folks.

Changed a Cu today. No rcd protection, Changed for a split way board. All tests were fine. Came to do Zs test on immersion heater - everything fine. Turned on DP switch to immersion and rcd tripped.

Had a good look at all cables for the circuit and all seemed fine. Disconnected immersion from switch, turned on switch and everything ok. No trip.

Is this a common problem with immersion heaters? It is quite old. Is this a case of just put in new element?

Many thanks
Harry
 
Does the immersion need to be on the RCD ?

They do tend to have lower resistance to earth because of the element
If the element tested ok for insualation resistance,perhaps it may be adding extra leakage to circuits already leaking which are on the same rcd and is then enough to tip it over the limit
It wasn't usual to have them on RCDs but it still should be healthy enough to do so
If its suitable remove the RCd protection
 
Thanks des.

I do have the option to place the immersion heater on an unprotected way. That would be ok then?

Sounds like the perfect solution to me.

cheers
harry.
 
Would it not depend on the route that the cable takes to the immersion heater? Would have to be surface mounted or below 50 mm.
 
Agree with Des there ! also rcbo's or if dual rcd board if element pans out ok try turning everything off then try just the immersion circuit and add circuits or try swopping to RCD 2. Also does the RCD pass the half current test ?

discon element and run a RCD ext lead from a socket then put a plug on immersion and plug and play ! if trips RCD change element !
 
Last edited by a moderator:

Reply to Immersion tripping rcd. in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
784
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
823
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
779
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock