Aquinas_Quark

Hello all,

Have just wired up a new Immersun 2; on switching the MCB supplying it, both earth leakage trips in my vconsumer unit knock off (strange as it's a split distribution setup - but BOTH trips go off). This also happens with the immersion heater disconnected from the Immersun output, ONLY mains in and the sensing clamp connected.
With the live conductor to the Immersun input removed from the MCB, I measure about 2Kohms between this live and earth - however if I ALSO remove the neutral to the Immersun from the neutral supply terminal block, the reading disappears.
SO I think it's my (very basic) meter - it is probably actually a small voltage across the live and earth on the Immersun input (with the live disconnected from mains), but ONLY when the neutral terminal is also connected to the mains neutral.
Strange! Anyone have any ideas? I know there is something between my neutral and earth because the earth trips go if I touch any neutral and earth in the house.
Any advice appreciated - it looks like a well-made unit and I would love to get it going!
 
if both are tripping then odds are definitely in favour of you wiring the neutral onto the wrong neutral bar in the CU.

Duh! I took it out one earth trip, in on the other! Working fine now - A BIG THANK YOU to all you above who responded - it's nice to know there is help when needed.

Regards & don't touch the brown ones...
AQ
 
You should have gone for s Solar iBoost as you wouldn't have got these problems then :teeth_smile:

Well with the cause of the error identified , I hope he WOULD have got those problems :)
 

Reply to immersun 2 giving earth leakage tripping in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
554
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
376
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock