Discuss Increasing supply, does DNO transformer look excessive? in the UK Electrical Forum area at ElectriciansForums.net

-Matt

-
Reaction score
152
Basically customer currently only has a 100A 3 phase supply, which is rather overloaded. Also has a 120KVA generator for a 55KW motor.

Im trying to get a larger supply so everything will run off the grid and not overloaded.

Ive spoken to the DNO in terms of trying to get a 400A supply.

DNO has asked for a list of large motors, and starting method, which is:

15KW motor 3 phase - S/D

11KW motor 3 phase - Soft start

36KW motor 3 phase - Soft start

15KW motor 3 phase - S/D

15KW motor 3 phase - S/D

55KW motor 3 phase - Soft start

Total power before diversity is around 180KW


There is HV overhead lines onto customer property, with current 100KVA pole transformer.

Was hoping for just a transformer change, along with new overhead cable, then 400A panel board etc at my end.

However the DNO want to install a 500KVA ground mounted sub station at a cost of £50,000.........

This seems rather excessive to me, and far more than the customer wants to spend...

The DNO are telling me its because of the starting current of the 36KW and 55KW motor.
They are using 164 starting amps for the 36, and 250A for the 55KW.
This doesn't sound right to me on a soft starter.

What do you guys think?
 
Maybe they've not noticed it says Soft start,
Or more likely their calculations don't take allowance for soft start.
Are these motors part of individual pieces of plant with random start, or making up a sequenced start system?

And presumably they've built in some spare capacity for the transformer.
 

Reply to Increasing supply, does DNO transformer look excessive? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

HiForum Thisall came about as I am looking to use a 3 phase motor with variablefrequency drive/VFD and started to get confused with 3...
Replies
9
Views
3K
Interesting discussion today with WPD, (My favourite DN0 :) ) with regards to extending an existing 3.68kW system. One pole, two overhead wires...
Replies
7
Views
2K
Ian-LS
I
M
Hey guys I've got 301 in two weeks time and I've been given some past papers will post some more soon hopefully. feel free to have ago and post...
Replies
16
Views
5K
Monks
M
S
I will post the answers on here in a few day or if you really want to know PM me and i will send them. Example Questions for 2382-10 1. The...
Replies
1
Views
2K
sxsparky
S
W
Hi everyone! Preparing to take exam later this month doing mock exam/past exam papers I'm stuck on some questions . Can anyone offer help on...
Replies
4
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock