Discuss Induction hob in the UK Electrical Forum area at ElectriciansForums.net

Status
Not open for further replies.
Well this one is 11.1kW and it too has a power manager function see page 31 of:

https://media3.neff-international.com/Documents/9001387749_B.pdf

Have you checked yours does not or are you not bothered preferring not to limit the maximum power by running a new cable etcetera?
Yes I can limit the maximum power of the hob but only up to the figure of 4Kw. Bit pointless having 15Kw of available hob element and setting the maximum to 4Kw. I will leave the hob to set its own maximum which in the case of my hob is 11.1Kw
Hence I need a circuit/s capable of handling 11.1Kw
 
[automerge]1577988230[/automerge]
in a void, with no insulation affecting heat dissipation, it's ref. C.

Was basing it on this

BS7671 17th Editon
Reference Method
Example of installation method
AIn conduit in an insulated wall with the conduit close to or touching the inner skin.
BEnclosed in conduit or trunking on or in a wall.
CClipped direct, or sheathed cables embedded directly in masonry, brickwork, concrete, plaster or the like (other than thermally insulating materials)
100Above a plasterboard ceiling covered by thermal insulation, insulation thickness less than 100 mm.
101Above a plasterboard ceiling covered by thermal insulation, insulation thickness greater than 100 mm.
102In a stud wall with thermal insulation with the cable touching the inner wall surface.
103In a stud wall with thermal insulation with the cable NOT touching the inner wall surface.
Has this cnaged in the 18th edition. My celing void has no insulation so reference method 100 is a worst case scenario
 
Last edited by a moderator:
Is that meant to be a sensible comment or not?
[automerge]1577988230[/automerge]


Was basing it on this

BS7671 17th Editon
Reference Method
Example of installation method
AIn conduit in an insulated wall with the conduit close to or touching the inner skin.
BEnclosed in conduit or trunking on or in a wall.
CClipped direct, or sheathed cables embedded directly in masonry, brickwork, concrete, plaster or the like (other than thermally insulating materials)
100Above a plasterboard ceiling covered by thermal insulation, insulation thickness less than 100 mm.
101Above a plasterboard ceiling covered by thermal insulation, insulation thickness greater than 100 mm.
102In a stud wall with thermal insulation with the cable touching the inner wall surface.
103In a stud wall with thermal insulation with the cable NOT touching the inner wall surface.
Has this cnaged in the 18th edition. My celing void has no insulation so reference method 100 is a worst case scenario

Ref 100 is 'covered by thermal insulation'. See Tel's post above.
 
None, no insulation at all plasterboard below floorboards above.

But method 100 is covered with insulation. I think I'm missing something here.
 
as there's no insulation, 100 and 101 are not applicable by definition
 
  • Like
Reactions: DPG
Have still not installed my Neff induction hob but is near. Was originally going to use 3phase but got battered on here so no. I have a 3 phase supply at home with 3 seperate Hager CUs. Red phase does the kitchen area, ring, lighting and a circuit marked cooker which fed a dual oven in 10mm2 via a 32 amp mcb. There is no RCD on the incomer just a 100 Amp switch. The sockets are via a 32amp RCBO, the lights via a 6amp MCB and the cooker via a 32 amp MCB. The original dual oven is to be replaced by 2 seperate ovens each of 13 amp max demand so total worse case is 26amp. The induction hob is limited to a maximum of 11kw approx 50 amp max. Easiest would be to run induction hob off the 10mm2 via an RCBO and run a 2.5mm2 from an RCBO to the ovens. Problem is I cannot find a 50 amp Hager RCBO. So could I run 2 of them in parallel? Alternatively change the 100amp switch for an RCD? Only problem I see here is Hager only do a 2 pole RCD with a 30mA trip at 63 amp max. If I want a bigger size 80 amp or 100 amp I need to go to a 100mA trip. Or should I just change the red phase cu?

No you can't take a phase from each seperate CU to feed the appliance.
No you can't connect two protective devices in parallel, especially not with residual current devices.
No you cannot use anything other than a 30mA residual current device to satisfy the requirements of additional protection. The regulations specify 30mA protection as this is the highest value at which most healthy people will probably survive an electric shock.

Unfortuantely your understanding of the electrical regulations and electrical safety seems to be lacking to the point that you could put yourself or others in serious danger so the best advice we can give you is to recommend that you engage an electrician to carry out the work.
 
I'm going to close this thread.

@Bogart , whilst we don't approve of members giving this advice, there is a time and place for it to be given and that time is now.

It appears from having a read of this thread that you lack the knowledge and understanding to conduct this work safely, therefore the best advice any professional on these forums can give you is to seek out the services of a qualified local electrician. We have a directory section (Find an Electrician | Electricians Directory - https://www.electriciansforums.net/local-electricians/), you may be able to find one there. Failing that get a couple of recommendations from family, friends and colleagues.
 
Status
Not open for further replies.

Reply to Induction hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
823
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
963
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
964

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock