Discuss Industrial Unit Earthing Arrangement - Lack of in the Commercial Electrical Advice area at ElectriciansForums.net

Back in the 80's having an earth in any size was a bonus given what I see from time to time. Spin is right though in terms of Western Power, they will not generally add a PME to a steel from. Normally they advise a TT.
 
Well took a little longer to get here but seems we’re running a 35mm earth cable through the wall and expanding an earth block that was hidden away in the distribution room, seems weird even back in the 80s that they just put a 6mm earth cable from the consumer unit to the isolator but guess it must have been ok back in the day!

Have you calculated the size of earth required?
 
I haven’t, the man in the know has, I thought he said 25mm before but he’s told me to get enough 35mm in to go through the wall into the meter cupboard where he’s connecting it in somewhere
 
I haven’t, the man in the know has, I thought he said 25mm before but he’s told me to get enough 35mm in to go through the wall into the meter cupboard where he’s connecting it in somewhere

What size is the incoming supply? You’ve shown a 100A cutout, but based on that you wouldn’t need anything bigger than a 16mm earth and actual calculation would probably prove the 6mm to be ok.
 

Reply to Industrial Unit Earthing Arrangement - Lack of in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
476
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock