ok so no trunking can clip to loft floor / beamsIf it is contained in trunking then 4.0 T&E is not suitable for 32A.
Discuss info re old shower isolator in the UK Electrical Forum area at ElectriciansForums.net
ok so no trunking can clip to loft floor / beamsIf it is contained in trunking then 4.0 T&E is not suitable for 32A.
Provided it is not prone to mechanical damage then yes.ok so no trunking can clip to loft floor / beams
thank youProvided it is not prone to mechanical damage then yes.
ive removed the bit where the cable will passWith the mention of a loft I'd expected the cable would at least pass through some insulation.
If this 6mm T&E cable is independent and straight from the DB.hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the isolator sw is feed with 6mm and fuse on board is a hager mtn132 /b32. the board has rcd . i would like to add two sockets to my loft . can i add a 4mm radial feed from the 6mm isolator in in to the loft for the 2 sockets i plan to set up a gaming room up there and a heater for colder months from my son . thanks for any help should add i am in the uk