I was taught to test R1+R2 at the furthest point, the theory being if you test at the most furthest point on your radial circuit and get an exceptional reading it means there are no breaks in the line or cpc.
This is how I was taught.
 
Measure at All points and record the highest as the circuits R1+R2, regardless if it’s not the last point such as the strappers forming the 2 way lighting to the landing light and switched both ways.
 
I would verify cpc continuity at all points. After all, the purpose of the test is to ensure that it is connected at all points and not just that there's a cpc path to the end of the circuit.

I would only conduct the Zs test at the end of the circuit though, having already proven continuity of the cpc.
 
When doing spot checks as QS I have observed that test results have been conducted at the last point of say a lighting circuit but as the permanent live in and out are at the switch then by testing only the last point of the circuit only confirms that the cpc is present at the last point.
I found that a light containing only a switch live and neutral did not have a cpc connected to the means of earthing as it had not been adequately connected at the switch point, so it’s important that it is done at all points.
This was a school job in which all lighting is metallic and as such ,exposed conductive parts.
 
Last edited:

Reply to Initial verification question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Not really a Question but its more a Point that the other Education Bodies out there than City and Guilds Granted most Employment agency dont...
Replies
3
Views
888
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
680
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock