Discuss Inspection of wiring to new industrial dish washer in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
26
Inspected a final circuit for a new dishwasher of the commercial type, rated at 4.3 kW, about 50M from the D/B. Final connection joint to the appliance flex comprises connector block in a dry wall box with lid lying on floor of commercial kitchen. C1, C2 or C3? Isolating switch on opposite wall 2M away un-labelled.
C2 or C3?
No paperwork left with client. Can client ask for this? No idea the cost of installation. Cable is 4 sq mm looped from a 2.8kW wall mounted water boiler on wall opposite where isolating switch has been sited. Cable to new dish washer run along corner of wall/floor behind three deep sink cast iron legs without containment. C2 or C3?
Comments please.
 
I agree it sounds like a poor installation but I would need to physically see it, some pics would be good.
 

Reply to Inspection of wiring to new industrial dish washer in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi Guys, First time posting but I've been commissioned with essentially running new cables from the head to 5 flats, due to the ground floor...
Replies
5
Views
3K
https://www.linkedin.com/pulse/can-you-really-test-circuit-6-dan-jackson-fiet incasee u dont use liked in heres the article in 2 posts An...
Replies
7
Views
2K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock