Hello. I am installing new storage heaters in a flat. I understand that they each need their own radial supply which goes back to the RCD protected E7 CU and they are each on their own MBC - probably 16amp. However, the heaters have an override switch for boosting during the day (not sure if this is just a fan or a separate convection heater). My question is this: do I need an additional circuit for the override boost or does an E7 CU work 24/7 but just has the cheaper electricity available in off peak (11-6)?


 
Notifiable, are you a qualified person? etc

1) The eco7 consumer unit does not supply all day
2) RCD protection depends on how the cables are run
3) You don't necessarily need to run back to the board for each storage heater, although I prefer to
4) The overrides are usually built in fan heaters. If the overrides are over 3kw then they should be on their own circuit (which you may as well do as you're running back to the board) on the 24 hour side

Alternately run a circuit to each storage heater from the 24/7 board and then have the override heater on a switched spur and the storage heater on a timer. Pending max load, type of meter etc
 
Thanks to you both. I did run two separate circuits in the end - as you both suggested. I am a sparky but have not been on the tools for quite a few years and so am a little rusty. I think I am going to be on this forum quite a lot in the coming months.
 

Reply to Installation of Storage Heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
770
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
576
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
865
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
165

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock