Going back on Friday for another look as he just told me he had kitchen revamped a couple of years ago and old jtn boxes left under floor boards above ? As kitchen fitters moved stuff. It Is old 60s wiring with no earth on light circuits, I know it gets better, but all fittings are class 2
 
Hi was asked to quote on new CU did checks first and 000ohms on neutral - earth on socket ring circuit, checked out and wiring needs replacing.customer still wants me to fit CU as he wants lighting, shower, garage etc to be RCD protected but put house ring on non RCD side in new CU. prob is he can't offered rewire old CU is broke (casing and MCB) what would you guys do and if you carried out job to make what is there safer what would you put on EIC ???? Thanks

First rule of this job....Never believe it when a customer says they can't afford something. I've fallen for that old chestnut when they are in threadbare clothes, sitting in an old patched sofa, only to find out later that they have more money than I'll ever dream of.
 
no need to rewire all of the circuit, just find the fault, disconnect from cu and break the ring and have a look where about the fault is. if thats 000ohms on continuity measurement may be a nailed cable or loose/burned wires touching metal back box somewhere
 
Is it an old rewireable fuse box? If so and your first and primary concern is the broken and dangerous fusebox itself then why not put in a new rewireable fuse box as a like for like replacment? Go back when the customer has more money and trace the fault and so on? Stage work in bits to allow customer to be able to afford it? Just a suggestion. Where there's a will there's a way :)
 

Reply to installation in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock