Discuss Installed a new C/U now have fault in the UK Electrical Forum area at ElectriciansForums.net

The reason we do an EICR before hand, or at the very least a site survey with some testing as the minimum, (as recommended I’m the best practice guide), is to find and iron out any problems prior to fitting a new board.

You should also be carrying out a full range of tests before energising the board and not just doing the bang test to bring it into service.
I’m guessing you charge for full EICR prior to advising a board change? I’ll do a pre survey of standard things like main earth, bonding, condition of accessories (age) advise customer that should any faults be found whilst testing then additional cost involved. Also you test it after completing consumer unite has been changed and this particular issue would have been picked up if done properly.
 
Hi - I’m assuming that one RCD is now tripping? Are the circuits in the new board on the correct N bar? If you post a pic it can often be seen if there’s a simple wiring error of that sort.
 
I’m guessing you charge for full EICR prior to advising a board change? I’ll do a pre survey of standard things like main earth, bonding, condition of accessories (age) advise customer that should any faults be found whilst testing then additional cost involved. Also you test it after completing consumer unite has been changed and this particular issue would have been picked up if done properly.

Not at all, and when I am conducting an EICR, it’s not a 40 minute drive by, full of LIMS and dodgy recommended remedial works used as a cash generator. It’s a thorough inspection that I charge accordingly for.

Now if you read my post properly, you’ll see i stated that a full range of tests needs to be completed prior to energising the board, IE, on completion of the board change and not just bang test it.
 
New here so sorry if posted in wrong place,
I have installed a new consumer unit as the title says it’s a split load rcd board, anyway to the point one of the rings seems to now have a neutral fault which is taking out one side of the board I have checked all obvious things, touched no appliances since installing only moved the existing wiring to the new board location etc. The thing that I can’t get my head round is I have continuity end to end but on both legs of the ring I have a short between live and neutral, all I can think of now is to IRT the circuit and see maybe this could be down the the install being 30 years old and degraded T&E over time? Maybe the inner cores are now touching? Seems funny tho because the old c/u was old but was still rcd protected so surely that would of seen the fault? And surely both legs wouldn’t have sustained damaged when I’ve moved the cables?
can give me details if required thanks in advance
Was it a 30mA RCD previously? It's possible that it was faulty and not picking up the fault.

As already mentioned, splitting the ring and testing is the only way to track down the fault. Then you can isolate it down to a particular length of cable or perhaps a fitting or two rather than taking everything apart looking for what might be something simple.
 
Think the general consensus is to test the existing installation prior to ripping the old board out to identify any faults that will leave you in a sticky spot with the new board....just when you’re looking to head home for a few we’ll earned beers ?
 

Reply to Installed a new C/U now have fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
296
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
587

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock