Discuss Installing 2x 9.5kw Red ring water heaters in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
hi guys
Went to have a look at a job to today where the customer is wanting two 9.5kw water heaters replacing for both the sink in the bathroom and the kitchen sink.
The property is a one bed flat with no gas supply hence the reason for the water heaters.
The property is supplied from a 60amp switch fuse-25mm tails
Other circuits include a shower at 9.5kw,hob at 5kw, 3xpanel heaters and general kitchen items.
this installation has being like this for many years apparently and not blown fuse.
What would you recommend is best option for this.
I’m trying to convince him to install a over sink water heater which are around 3kw max in the bathroom to reduce load but do you still think this is too much.
 
I have found the 2kw steeple ones from denmans do a decent enough job, especially for a 1 bed property. 9.5kw is way too much for that flat. Have you not considered the instant hot water heater taps that you can get that do same job but replace the mixer tap? they are in Denmans aswell? might be a better fit for the kitchen?

tap.JPG
 
I have been dealing with almost exactly the same but in a holiday cottage. Continual complaints of no flow in the showers, lights dimming when the showers are used etc.
We have just replaced it all with an electric boiler and wet radiators with stored hot water. Customer very pleased
 
Hi, does is the stored hot water heated indirectly by the electric boiler, or does the cylinder just use immersion? Just curious to know the recovery time on that sort of set up, could be a useful solution for some situations. Cheers
 
Either or both! We put a horizontal unvented quite large cylinder in the attic, mains water pressure being very good. The cylinder has facility for a standard immersion but we didn't bother, we only used the indirect coil from the boiler.
Whilst electric heating is quite expensive there are cost savings in no annual gas check required, far less mechanical parts to go wrong etc.
If recovery times could be an issue, increase the size of the tank so you have more stored. Modern tanks are quite efficient
 

Reply to Installing 2x 9.5kw Red ring water heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
230
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
173
Hi all, I’ve been given 3 flats to re wire and i was looking for advice on the correct size Swa to use. There will be 3 meters installed by the...
Replies
12
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock