Hi first post diy, I have a Y plan system ,the system is quite old and fully pumped with header tank in loft. I want to connect a Honywell DT92E wireless room stat .
The Honywell receiver BDR91 Has the Terminals NLL ABC the information I would like, is do I make up a little link wire for connecting the second L to A

Thanks in advance T.J.
 
Hi first post diy, I have a Y plan system ,the system is quite old and fully pumped with header tank in loft. I want to connect a Honywell DT92E wireless room stat .
The Honywell receiver BDR91 Has the Terminals NLL ABC the information I would like, is do I make up a little link wire for connecting the second L to A

Thanks in advance T.J.

No the receiver requires a permanent live to terminal L, neutral to N, Ch on from programmer connects to terminal A, terminal B connects to white on 3port valve.
 
To Leesparkykent Thank you very much for the quick reply ,you have put mind at rest now .all the best T.P.
 

Reply to Installing Honywell Wireless DT92E Room Stat in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
619
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
Replies
0
Views
1K
Reaching out for some help/guidance and sanity check. Apologies in advance for the long post, but wanted to make sure it was clear. Thanks in...
Replies
0
Views
959

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock