  1. les24preludes
    Offline

    les24preludes EF Member

    Location:
    London
    New kitchen - induction hob at 7.4kW (32amp) and oven at 3.6kW (16amp) max ratings. Existing outlets are:
    1. 45amp fused cooker circuit
    2. fused socket off ring main (32A fuse)

    Can both oven and hob be connected off the one 45amp cooker circuit? That's right up to the maximum.

    Or can the oven be connected to the ring main?

    Or does the oven require its own circuit - that would be an extra installation and need rewiring to the fuse box.
     
  2. Midwest
    Online

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Firstly OP, are you an electrician? If not how is this work being carried out?
     
    • Like Like x 1
  3. les24preludes
    Offline

    les24preludes EF Member

    Location:
    London
    Hi - I'm not a qualified electrician but I build a lot of electronics, so familiar with calculations and wiring stuff up. What I want here is a correct plan so I know what the installation is likely to be and how it affects the layout of the rooms and units.

    I've read a lot of posts on this already, and you might be surprised how much they vary. For example, even electricians say they're fine with twin and earth, where cooker manufacturers always specify heat resistant cable. I already bought Butyl coated 6mm cable for the induction hob, which meets the standards of heat resistance.

    I'm hoping this forum can offer me a more definitive answer to this fairly common question.
     
  4. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Hob and oven will be fine together on a 45A circuit (providing that the existing cable is properly protected by a 45A OCPD).
     
  5. Midwest
    Online

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    There are some variables, and sitting from here its to easy to take things for granted. OP there is a factor called diversity that can be applied to these circuits & appliances, but there is also a recommendation about ovens/hobs etc, with a load of more than 2kw having their own radial.

    The first question would be exactly what does your 45amp fused cooker circuit consist of?
     
  6. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Absoluutely. 45Amp is quite an unusual rating for a circuit (not unknown, but unusual). What makes you think it is 45 amps?

    So, need to know
    1. the size of the fuse or MCB in the consumer unit that protects this "cooker" circuit
    2. the size of the cable

    Two other items

    Well no it isn't/ When calculating the maximum demand for circuits we use a technique called 'diversity'. This allows us to reduce the assumed max current that a domestic oven etc will use in practice. this is based on the fact that everything in an oven/hob etc is thermostatically controlled so that, statistically, the appliances never pull the quoted maximum current.
    There's an interesting article on this at TLC Electrical Supplies - https://www.tlc-direct.co.uk/Book/6.5.2.htm

    Ah, no.

    But it is likely that both can go on your existing circuit - depends on your answers to the questions, above...
     
  7. les24preludes
    Offline

    les24preludes EF Member

    Location:
    London
    Good points. The 45 amp circuit comes from the fuse box, where there's a 45 amp fuse, into a wall mounted switch with neon (no fuse). The wiring here is 5mm OD overall including insulation - I haven't looked up specifications yet to determine if this is 6mm or 10mm. Should be 10mm, so I hope that's right. The same diameter wiring goes down to what looks like a 45 amp junction box on the wall under the worktop. This is a usual single size junction box, i.e. 850x850mm.

    If the supply were split into hob and oven, I'm thinking it would need a larger 3-way junction box. I'm expecting the 5mm OD cable to be 10mm, and from there it would go to a 6mm for hob and 2.5mm for oven. The butyl cable to the hob is 15mm OD including insulation - pretty solid.
     
  8. hightower
    Offline

    hightower Guest

    Send me a photo of that 6mm cable connected to the hob/oven when you're finished, when many are designed (and ask in MI) for 2.5mm. You'll do well to terminate a 6mm cable in to most of the hobs/ovens I've come across.
     
  9. les24preludes
    Offline

    les24preludes EF Member

    Location:
    London
    Sigh.... absolutely. This is an AEG hob and while they specify 6mm heat resistant cable it wouldn't surprise me if it's too thick to fit properly, just like you say. Haven't come to that bit yet.
     
  10. Midwest
    Online

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    OP, not sure how it works, but you would have been better posting in the DIY section. Bit late now.

    There's too much guessing (5mm OD cable to be 10mm) to be sure you have a 45amp supply, i.e. 10mm cable. Most cooker radial supplies are 32amp MCB & 6mm 6242y cable. It may be you have a 10mm cable, but the MCB might have been previously upgraded to 45amp, but not the 6mm cable.

    Allowing for diversity & installation method, a 32amp supply may be suitable for you appliances, it may not. The heat resistance cable, is only necessary for the final connection to the appliance (if the manufacturer recommends it), and may not have to be 6mm in size, flexible cables have differing ccc to 6242y cables.

    In all honesty, you might wish to consider employing an electrician to carry out this work (looks like a kitchen refurb anyway). Otherwise you might have a supply that's too small, or end up installing a larger cable that is unnecessary. If you do end up with a new circuit, this is notifiable to the LBC. And if the any additions/alterations cables are installed in walls, it may require additional protection by RCD. Use an electrician. :)
     
    • Like Like x 1
  11. les24preludes
    Offline

    les24preludes EF Member

    Location:
    London
    Thanks, Midwest. Evidently the first thing I need to know is what cable is in cooker radial supply. If the OD of the cableing is 5mm, looks like 6mm to me. I've been looking up specifications and the OD of a 10mm earth wire is at least 6.1mm for the earth wire:

    20147721 | Prysmian 6491X H07V-R Conduit Cable, 10 mm² CSA, , 750 V Green/Yellow PVC 100m | Prysmian - http://uk.rs-online.com/web/p/conduit-trunking-cable/0381292/

    In fact while pos and neg are 5mm OD, the existing earth is a bit less than that. So looks like I can forget running hob and oven off the existing cooker supply, which looks like 32 amp with a 45 amp fuse. But that's OK for the hob at least.

    That leaves the oven - 16 amps. There's a mains socket under the worktop with a fused switch above which comes off the ring mains. So the question would be whether - considering diversity - it would be wise to run the oven off that. There's space in the fuse box for one more fuse, and it wouldn't be too disruptive to install another supply to the oven. I just want to know if it's necessary to meet wiring regs.
     
  12. Leesparkykent
    Online

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    With diversity taken in to account the load comes to roughly 21A. How is the 6mm cable cooker supply installed?
     
  13. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    If it is T&E the cpc (earth) for 6.0 will nearly always be a solid conductor. The 10.0 will be stranded.
     
    • Like Like x 3
  14. les24preludes
    Offline

    les24preludes EF Member

    Location:
    London
    Looked again, and you're right - the earth wire is solid. Pretty much confirms that the "cooker" supply is 6mm, so 32 amp. So hob only.
     
  15. Leesparkykent
    Online

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Not necessarily...How is the 6mm installed. Does the route encounter any insulation?
     
    • Like Like x 1
Loading...
Similar Threads - Installing induction hob+electric Forum Date
Installing Electric Hob Electrical Forum Jun 4, 2018
Installing earth rod Electrical Forum May 30, 2018
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. induction hob supply

    ,
  2. correct way to install an electric oven and separate electric hob

    ,
  3. wiring induction hob and oven

    ,
  4. connecting induction hob and oven,
  5. installing a cooker and seperate hob circuit,
  6. how to connect hob and two ovens to electric,
  7. electric hob and oven on same circuit,
  8. ways to wire hob and cooker
Electricians Directory Post a Domestic Job Post a Commercial Job