Yes that's that new approved test......Licking Of Conductors
Brilliant :clap::clap:
Low Ohm Continuity
All circuits, bar circuit 9, individually, came out as >999 M ohm across L-N, L-CPC, and N-CPC. it was only when I connected them all up to the RCDs, and doing a collective test, that the L-N came out as 0.06 M ohm on RCD 2 / Circuits 5-9.
With circuit 9 disconnected, circuits 5-8 all read >999 m ohm, and Circuit 9 caused the drop. testing circuit 9 individually across its respective conductors gave the following:
L-N = 600 M ohm
L - CPC = >999 M ohm
N - CPC = >999 M ohm
I got in a spin when connecting it up and got that 0.06 reading across L-N as a "collective".
Additionally I can't connect the CCU to the main earth as the supply cable hasn't been installed by the DNO yet.
I did leave an extractor fan connected on circuit 9, although off at the 3-pole isolator. As its a load, I should have really pulled the wires out. It had been a long day and I was panicking a bit when I started this topic ...
Cheers for all the replys, you have all given me fresh hope!