I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?
 
I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?

Hi Dave
Why can't you get to the top of the floodlight? In the mean time try gaining access to the trainee section, as a trainee you will get more help and less agro from the members, the trainee section has mentors to help you with problems. PM PaulM he will help you with access I'm sure
 
short circuit between live and earth

By definition, this cannot be normal. It will eat the fuse or MCB at switch-on. Do you genuinely mean a short-circuit? That is not the same as a low reading on an insulation tester.
 
If you have 0.14 ohms on low ohm continuity scale, then you have a short L-E. Like already said above you would blow OCPD immediately. You need to gain access to investigate further.
 
Surely if that was the case, the floodlight wouldn't be working. At the bottom of the column is two 6A fuses and the floodlight is supplied from TT installation with 300mA RCD on the supply. Wouldn't these have operated or blown if there was a fault. Was thinking N and E may be linked within the floodlight
 
Surely if that was the case, the floodlight wouldn't be working. At the bottom of the column are two 6A fuses and the floodlight is supplied from TT installation with 300mA RCD on the supply. Wouldn't these have operated or blown if there was a fault. Was thinking N and E may be linked within the floodlight

It might have been pertinent to mention that it was still working in your OP!

If it's working then there is no fault??? or have I missed something?
 

Reply to Insulation Resistance of floodlights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
588
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
663
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
734

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock