Discuss Insulation Resistance of floodlights in the UK Electrical Forum area at ElectriciansForums.net

D

Davetherave

I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?
 
I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?

Hi Dave
Why can't you get to the top of the floodlight? In the mean time try gaining access to the trainee section, as a trainee you will get more help and less agro from the members, the trainee section has mentors to help you with problems. PM PaulM he will help you with access I'm sure
 
short circuit between live and earth

By definition, this cannot be normal. It will eat the fuse or MCB at switch-on. Do you genuinely mean a short-circuit? That is not the same as a low reading on an insulation tester.
 
If you have 0.14 ohms on low ohm continuity scale, then you have a short L-E. Like already said above you would blow OCPD immediately. You need to gain access to investigate further.
 
Surely if that was the case, the floodlight wouldn't be working. At the bottom of the column is two 6A fuses and the floodlight is supplied from TT installation with 300mA RCD on the supply. Wouldn't these have operated or blown if there was a fault. Was thinking N and E may be linked within the floodlight
 
Surely if that was the case, the floodlight wouldn't be working. At the bottom of the column are two 6A fuses and the floodlight is supplied from TT installation with 300mA RCD on the supply. Wouldn't these have operated or blown if there was a fault. Was thinking N and E may be linked within the floodlight

It might have been pertinent to mention that it was still working in your OP!

If it's working then there is no fault??? or have I missed something?
 
If the IR test was at 250v and no higher it's fairly unlikely it's an MOV, the clamping voltages are usually higher than that unless they're the type sometimes used in telecommunications and RS232 and other comms systems.
 
0.14 what, bannanas,ohms, megohms, pineapples?
There is no such thing as a dead short. Its a fault of negligible impedance that exists.
 
Yep never heard of a MOV
not just me then Solo.

MOV's are used as lightning and surge protection all the way through the network from transmission lines to being internally installed in control panels and appliances. They come in a multitude of guises.
All these are MOV based protectors and they'll all give low IR reading with a megger tester set on a high test voltage.

1.jpg 2.jpg 3.jpg 4.jpg 5.jpg 6.jpg

Many appliances have an internal filter circuit PCB which has MOV's on it amongst other things.

10.jpg
 
This is daft. We're 26 posts into a thread called "Insulation resistance of floodlights" and the OP still hasn't told us what the insulation resistance of his floodlight is. It could be anywhere between 0.14 ohms and 0.14 megohms, which is the same ratio as that between a pint of beer and 24 articulated tanker lorries of it.
 
0.14 ohms

Well if it's really 0.14 ohms L-E and the light works, the CPC must be O/C somewhere and there is a risk of exposed bits being live. If this is not obvious to you, I suggest studying a bit more about testing before undertaking this kind of work.
 
OK so you walked over to a random floodlight that was WORKING and thought hummmm im going to do an insulation resistance test on this working light????
WHY MATE ???
Alternatively if you are part of the electrical trainee Nerd Herd then leave the flood well alone and let it continue working normally as it is before you do F it up !!
 

Reply to Insulation Resistance of floodlights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
646
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
588
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
720
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock