Insulation Resistance of floodlights

Discuss Insulation Resistance of floodlights in the UK Electrical Forum area at ElectriciansForums.net

D

Davetherave

I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?
 
I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?

Hi Dave
Why can't you get to the top of the floodlight? In the mean time try gaining access to the trainee section, as a trainee you will get more help and less agro from the members, the trainee section has mentors to help you with problems. PM PaulM he will help you with access I'm sure
 
short circuit between live and earth

By definition, this cannot be normal. It will eat the fuse or MCB at switch-on. Do you genuinely mean a short-circuit? That is not the same as a low reading on an insulation tester.
 
Surely if that was the case, the floodlight wouldn't be working. At the bottom of the column is two 6A fuses and the floodlight is supplied from TT installation with 300mA RCD on the supply. Wouldn't these have operated or blown if there was a fault. Was thinking N and E may be linked within the floodlight
 
Surely if that was the case, the floodlight wouldn't be working. At the bottom of the column are two 6A fuses and the floodlight is supplied from TT installation with 300mA RCD on the supply. Wouldn't these have operated or blown if there was a fault. Was thinking N and E may be linked within the floodlight

It might have been pertinent to mention that it was still working in your OP!

If it's working then there is no fault??? or have I missed something?
 
If the IR test was at 250v and no higher it's fairly unlikely it's an MOV, the clamping voltages are usually higher than that unless they're the type sometimes used in telecommunications and RS232 and other comms systems.
 
Yep never heard of a MOV
not just me then Solo.

MOV's are used as lightning and surge protection all the way through the network from transmission lines to being internally installed in control panels and appliances. They come in a multitude of guises.
All these are MOV based protectors and they'll all give low IR reading with a megger tester set on a high test voltage.

1.jpg 2.jpg 3.jpg 4.jpg 5.jpg 6.jpg

Many appliances have an internal filter circuit PCB which has MOV's on it amongst other things.

10.jpg
 
This is daft. We're 26 posts into a thread called "Insulation resistance of floodlights" and the OP still hasn't told us what the insulation resistance of his floodlight is. It could be anywhere between 0.14 ohms and 0.14 megohms, which is the same ratio as that between a pint of beer and 24 articulated tanker lorries of it.
 

Reply to Insulation Resistance of floodlights in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top