Today I got 0.11 Mohm L-N>E at 250v then the same at 500v on a 6amp lighting circuit wired in the 70s which is the only lighting circuit for the house. Customer did not want me to remove the lamps. I forgot to ask or see a bell transformer or aerial booster. No faults known to the customer. MCB not tripping. No RCD. I broke the circuit down and tested L-N at 250v dead short 0.0 Then L-E N-E at 250v and 0.11 for both... I keep telling myself it must be something connected... Or is it a fault. Indicated further investigation on the MWC. Spending tonight racking over what it could be. Also how do you guys explain this to a customer without waffling the entire bs7671 to them whilst using a new piece of cable to explain cable deterioration and the benefit of having an RCD with out them thinking that your having them on.
 
the L-N reading will be through the load/s. as tis reading is too low for an IR test to read, you'll get the same readings L-E and N-E. to determine which it is, you need to remove the load/s/lamps etc
 
Also how do you guys explain this to a customer without waffling the entire bs7671 to them whilst using a new piece of cable to explain cable deterioration and the benefit of having an RCD with out them thinking that your having them on.

I find the best thing to do in these situations, is to suggest sitting down with a brew, then slipping an E in their tea, after you've just pointed out something behind them.
Twenty minutes later...they'll agree to anything.
 
Two, I had one disconnected which was the reason to be there and the other halogen flood had the lamp in high up.

more than likely to be a load then...

Assuming that the above is in answer to "Any outside lights?", I would suggest that the first place to look for the 0.11M L+N to E is an existing outside light with water ingress.
 
tested L-N at 250v dead short 0.0
0.0 what? Ohms? Megohms? Why would you call it a dead short?

"0.0" means 0 +/- 0.05. If that's the number in the window of the MFT that could be +/- a few counts, let's be generous to the MFT and say one count. So if you mean megohms, all we know is that the reading is less than 150 kilohms, which will pass a spectacular 1.5mA at 230V and consume 1/3 of a watt. So far from being a dead short (which would have tripped the MCB) it could be a load so tiny that it wouldn't light a torch bulb and half a dozen of them running to earth wouldn't trip an RCD.

By dead short I would infer two pieces of wire touching - 0.0 ohms is more like it!

Now 0.11 megs to earth is a fault. Whichever way you look at it, that is a fault. See above re. wet stuff...
 

Reply to Insulation resistance on a lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
Downstairs lighting is tripping rcd. Circuit has 4 chandeliers with multiple bulbs and led downlights in the bathroom. Can I just test IR on...
Replies
3
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock