Discuss Insulation resistance test issue in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
101
Back in 2013 I had a Domestic Electrical Installation Condition Report done on my rented property - nothing horribly major but one thing I didn't understand...

I had a C3 code for "0 ohms readings for I.R test for sockets & lighting (unable to remove all loads sockets, lighting had electronic dimmers)"

I didn't do anything about this at the time, but 5 years on I'm thinking that cables don't improve with age so perhaps I should get the insulation testing done this time.

So...
1) Yes I have some electronic dimmers, so how do I overcome this? Do they need to be taken off to do the IR testing? And do I need to put ordinary switches back on temporarily, or can I just unscrew the live cable, do the test and put the switches back?
2) I don't understand how sockets would have been a problem, surely it's easy enough to just unplug everything. Was the tester just being lazy, or is there another problem that isn't really being explained?

Thanks
Phil
 
Which was the 0MOhms recorded? L-N, L-E or N-E?

If L-N then it is more than likely the dimmers, however this shoukd have been labelled Lim and a limitation agreed before hand if all dimmers were not to be rwmoved frpm the circuit prior to testing.
 
If not possible to remove something that may be damaged (lighting transformers, 13a sockets with USB, etc) by a 500V Insulation Resistance test, your electrician will common L&N and test to E at 500V and then test L to N and L to E at 250V
 
Report attached, I have:
Lim on most L-N
0 on all N-E and some L-E

Scope would have been agreed by my agent, I doubt if they would have understood what it means anyway. I doubt if dimmers were removed.

Would that also apply to switches with PIRs built in (garage)?

Thanks
 

Attachments

  • 2013-11-04 Electrical Condition Report.pdf
    19.7 KB · Views: 51
Chris - attached. Main job is to replace the CU, mains tails and bonding all part of same job in the garage, I think. I've dealt with the small things. This is item 7.

Tony - back in 2013 I wouldn't have had any USB sockets, but do now! Some fluorescent lights (the big old tubes) with starters etc back then, but now some LED strip lights.

This is sounding like just the IR test is shaping up into a big job if I have to disconnect all the dimmers, USB sockets, LED lights etc.?
 

Attachments

  • 2013-11-04 Electrical Condition Report p2.pdf
    15.7 KB · Views: 33
Im not after the limitations or i woukd be asking for page 1. Im after the deviations that he has found on his EICR.
Limitations were :
- Unable to disconnect all connected loads to carry out L-N insulation resistance testing,
- No lifting of floor boards or inspection of loft space

Thinking about it, "Unable to disconnect" seems a strange thing to say. Of course it would have taken more time (which I'm sure would have been charged) but I don't see why he would have been unable to do it.
 
IR Test should have been done by linking the L&N and testing to earth in this case IMO. By the looks of all the neutrals been 0, he hasnt bothered to disconnect the neutrals when IR testing.

Not. Picked up the high r2 reading on one of the rings or the oversized protective device on the water heater (although if only a fused spur would be a C3). Low IR in my book is a C2 as it is potentially dangerous.
 
Im not after the limitations or i woukd be asking for page 1. Im after the deviations that he has found on his EICR.
Ok but a deviation is a design decision made that doesn't comply with the regs but provides an equivalent level of safety to that which would comply.
If they were listed on the eicr, it would only be a comment referencing the eic. If a non compliance was found it would be given a classification code depending on what kind of danger it posed.
 
I think this time round I'll be there when it's done. Sounds like I need to be!

S'funny, 20-30 years ago when you hired an expert you just left them to get on with it, nowadays you need to have a much higher degree of understanding to even define the job that needs to be done. But that's getting a bit philosophical...

This is for my house in UK, but where I (mainly) live in Azerbaijan all tradesmen are called "meister" - but most of the time I know more about how to do the job than they do.
 
Maybe they have TNC installations in Azerbaijan?
This is my house in Reading!

In Azerbaijan many, even most, houses are wired without earth cables at all. I have a 3 phase supply with 4x16mm aluminium cores. I put two large earth rods in the garden. The house is wired with T&E and CU imported from the UK, apart from first fix I did most of it myself, including learning to strip 4x35mm SWA.

But over in the thread where you post photos of bad installations I added some pics of the usual standards here.
 

Reply to Insulation resistance test issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
603
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
718
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
840

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock