If some of the circuits of a shower block for a big site have been tested for insulation resistance during constuction.

what is the possible effect that insulation resistance testing the whole installation when completed have on values obtain on completion compared with for those circuits when tested individually?
 
what is the possible effect that insulation resistance testing the whole installation when completed have on values obtain on completion compared with for those circuits when tested individually?


The IR test results will come back lower, because you have more cables and therefore more leakage paths.

As an additional piece of information, it may not be possible now to do the L-L IR test, only the L+N to E test, either due to vunerable equipment and/or Neon indicators.
 
most of the questions im on the right track or already no it, just want to check it with senior electricians like yourself

I suggest you start putting your answers, first of all, in the thread after your question each time, people will tell you if you are right or wrong.
All you are doing is alienating yourself from people willing to help, it seems like you want an easy way of getting homework answers.
 
Paulthemagpie, think of resistors in parallel.
What's the value expected collectively if you have four circuit's measuring 350Mohm, 320Mohm, 290Mohm and 176Mohm?
 
Sorry chaps,

I did not realise it was a homework question, I actually thought it was a genuine request for help.

I don't usually just give out the answers, and like most of us on here just normally give helpful hints, or references.
 
Paul, apart from anything else that has been said above, if you take a little time to think this one out you will get the answer. It's easier than you think
 

Reply to insulation resistance testing question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
589
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you...
Replies
0
Views
446
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
824
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
501
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
664

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock