Sb8389

-
Reaction score
25
Hi guys,
i have always wondered when doing insulation resistance testing is there a test you can do to see if there are any loads still connected (ie neons,equipment) to see if the readings are true or through loads connected in the circuit.
 
Cheers for the info guys. If a load was connected would it only effect Live-Neutral readings and not Live-Earth and Neutral-Earth or would it. I know these are basic questions for you guys but never really asked the question.
 
Cheers for the info guys. If a load was connected would it only effect Live-Neutral readings and not Live-Earth and Neutral-Earth or would it. I know these are basic questions for you guys but never really asked the question.

Yes it would. You would also be testing the connected equipment. For the sake of your tests you want to eliminate that. However it can also be very useful to carry out a global IR with it all connected under certain circumstances.
 
Cheers for the info guys. If a load was connected would it only effect Live-Neutral readings and not Live-Earth and Neutral-Earth or would it. I know these are basic questions for you guys but never really asked the question.

Do a test on your own place with half the "socket" load items plugged in, then gradually unplug them and watch the results change!
 
Possibly, depends on the appliance , some loads might not register at all on any of the tests , other appliances may have some leakage to earth , Always best to unplug everything and ask the customer what they have and go round with them , you have to be careful and not just rely on readings to tell if everything is unplugged , anything electronic you have to watch , always use 250v range first on all 3 tests , but still if this reads clear and theres things still plugged in ,and you then try 500v tests its you or your insurance thats paying for damaged appliances ..
 
However it can also be very useful to carry out a global IR with it all connected under certain circumstances.
A global IR with what all connected? Loads?
How would it be useful?
What would it prove?
You would get the lowest reading possible. IE reading through the first load. What possible use could this reading be?
Under what circumstances would this be useful?
 
Would testing live and neutral together connected to earth bypass any loads still connected and give a true reading of the circuit or is it just for the purpose of eliminating damaging equipment.
 
Would testing live and neutral together connected to earth bypass any loads still connected and give a true reading of the circuit or is it just for the purpose of eliminating damaging equipment.
Have a think about what you're asking mate, I'm not saying it's a bad question here but if you think about it the answer will become clear.
If I gave you it on a plate you'd have learnt nowt :)
Sorry for being a git :)
 
A global IR with what all connected? Loads?
How would it be useful?
What would it prove?
You would get the lowest reading possible. IE reading through the first load. What possible use could this reading be?
Under what circumstances would this be useful?

L&N-E 250V IR Before a consumer unit change when there was previously no RCD protection. Then test with them disconnected. It highlights if there is any earth faults on the w/m, d/w immersion etc etc in.
 
The I/R tests are to be done as per GN3
, this requires all appliances isolated/removed , the readings required are of the circuit not the loads as well , what you suggesting is really a way of trying not to damage appliances , this is not the point and besides you could still damage appliances anyway..
 
Last edited by a moderator:
Right trev I'm thinking that testing live and neutral ensures you are putting the same voltage down both conductors so they are of the same potential eliminating damaging any equipment, am I on the right track
 
Sorry mate, I meant in addition to carrying out disconnected, otherwise it would be obviously pointless :) I updated after I posted.
Sorry TJ but you're going to DC all loads, test, then reconnect them all and test again to see if there's any appliance problems?
NAAAAH that's bolox again:)
A It's wasting time and effort
B What's the point? Unless you've got a sideline in appliance repairs of course
 

Reply to Insulation resistance testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
820
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
392
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
663

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock