Search the forum,

Discuss Insulation test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

An IR test can be performed at any point in the circuit so long as it is all continuous (i.e you do not remove the cables from the socket) , however if the cables are still connected in the consumer unit then they will also be (for Neutral and earth) connected to the other circuits, whilst it is advisable to have the earth still connected to ensure there are no other earthed parts that may short to line or neutral, having the neutral connected will apply 500V to one side of the other circuits and this may give incorrect results and possibly cause damage to connected equipment. Also if the circuit is only switched off at the circuit breaker and the main switch is still on there will be a neutral earth connection either at the service head (TNCS) or at the sub station (TNS) which will give false results.
 
Hmmm, probably not the best place to do an IR test from, for the reasons Richard states.
You're not thinking of doing R1R2 tests from a socket as being wrong? Some people insist it's wrong.
Perfectly fine I say.
 
An IR test can be performed at any point in the circuit so long as it is all continuous (i.e you do not remove the cables from the socket) , however if the cables are still connected in the consumer unit then they will also be (for Neutral and earth) connected to the other circuits, whilst it is advisable to have the earth still connected to ensure there are no other earthed parts that may short to line or neutral, having the neutral connected will apply 500V to one side of the other circuits and this may give incorrect results and possibly cause damage to connected equipment. Also if the circuit is only switched off at the circuit breaker and the main switch is still on there will be a neutral earth connection either at the service head (TNCS) or at the sub station (TNS) which will give false results.
I was thinking to test the I.R.of the whole installation..main switch off ,cbs on and useing a shorting plug to join neutral and earth at the other half of the double socket. Of course continuity testing first...and then operating the 2 ways and all that,Same deal for testing at the board if there's electronic stuff that might get fried disconnect /test at 250 .
 
Last edited:
Hmmm, probably not the best place to do an IR test from, for the reasons Richard states.
You're not thinking of doing R1R2 tests from a socket as being wrong? Some people insist it's wrong.
Perfectly fine I say.
I dont see any problems either from doing the ring tests at a socket either..in fact sometimes its handier can use the terminals to cross link for fig.8 tests..sometimes its quite difficult to disconnect in the board and be sure that you have the right set of neutrals.Also in a socket its usually easier to distinguish the ins and outs
 
Nothing wrong with testing in ways other than 'to the book', providing that you think through all the consequences and fully understand what you're doing, which clearly you do. I agree that ring continuity is often much easier at a socket than the board.
 

Reply to Insulation test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
735
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
665
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
729
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock