I was thinking to test the I.R.of the whole installation..main switch off ,cbs on and useing a shorting plug to join neutral and earth at the other half of the double socket. Of course continuity testing first...and then operating the 2 ways and all that,Same deal for testing at the board if there's electronic stuff that might get fried disconnect /test at 250 .An IR test can be performed at any point in the circuit so long as it is all continuous (i.e you do not remove the cables from the socket) , however if the cables are still connected in the consumer unit then they will also be (for Neutral and earth) connected to the other circuits, whilst it is advisable to have the earth still connected to ensure there are no other earthed parts that may short to line or neutral, having the neutral connected will apply 500V to one side of the other circuits and this may give incorrect results and possibly cause damage to connected equipment. Also if the circuit is only switched off at the circuit breaker and the main switch is still on there will be a neutral earth connection either at the service head (TNCS) or at the sub station (TNS) which will give false results.
I dont see any problems either from doing the ring tests at a socket either..in fact sometimes its handier can use the terminals to cross link for fig.8 tests..sometimes its quite difficult to disconnect in the board and be sure that you have the right set of neutrals.Also in a socket its usually easier to distinguish the ins and outsHmmm, probably not the best place to do an IR test from, for the reasons Richard states.
You're not thinking of doing R1R2 tests from a socket as being wrong? Some people insist it's wrong.
Perfectly fine I say.
Sorry meant to write neutral and live.Missed the cutoff time to editYou want to short out neutral to earth?
Why?
Reply to Insulation test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
We use essential cookies to make this site work, and optional cookies to enhance your experience.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.