Discuss Interesting cutout and apparent lack of earth in the UK Electrical Forum area at ElectriciansForums.net

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
Called to house customer wants new shower fitted, 2 extra sockets in conservatory and possibly the board upgraded.
No rcds on the board and when the smart meter folks came before christmas they refused to fit one due to the old cut out and fuse carrier cracked and old DNO(wpd) have been and fitted a new cutout and it appears the installation has no acceptable earth.
There is a connection of sorts to a sheathed cable at the top of the board which doesnt terminate inside. Its cut back and looks from earlier wiring. Can not locate the end of this cable.
The incoming supply looks as if it was Tns and there is a small cable cut back and wrapped up. Done by dno apparently customet says!
The new cutout looks as if it is set up for pme but waiting for confirmation.
Get a ZS on ring circuit of 21 ohms. First thought was TT but no rod to be found in or outside. Disconnected the one bonding cable to gas and get 21.9 ohms so not a vast difference.
DNO have told customer its all safe and no issue!! No rcds so the zs is way over the acceptable limit.
Considering putting a rod in myself but a damn pain as board is in middle of the house so a long awkward cable run.
Will be changing the board early this year and doing other bits but need things sorted first.
Thoughts?
I recall @Vortigern had conversations with WPD about earthing and cut outs so would be good if he can update us before i call them and query things.

20190105_100825.jpg


20190105_101244.jpg


20190105_100726.jpg


20190105_100757.jpg
 
The incoming supply looks as if it was Tns and there is a small cable cut back and wrapped up.

If that's the short bit of VIR formed into a loop, and it's connected to the lead of the service cable, it's probably a very good earth. As the supplier did at one time supply it, they are probably obliged to maintain it, unless they provide TN-C-S instead, so probably more legit than making off a new earth to the lead.

The outgoing cable above the board with flexible braid overall is an old Octopus-style cable. Rare to see one of those by itself these days.
 
If that's the short bit of VIR formed into a loop, and it's connected to the lead of the service cable, it's probably a very good earth. As the supplier did at one time supply it, they are probably obliged to maintain it, unless they provide TN-C-S instead, so probably more legit than making off a new earth to the lead.

The outgoing cable above the board with flexible braid overall is an old Octopus-style cable. Rare to see one of those by itself these days.
Its not connected to the incoming service head. The old earth cable from the head is about 6 inches long and coiled up below the new henley.

I did remove part of the insulation on the coiled cable below the cutout to do a Ze. Got 0.68 ohms. Not brilliant but with TNS limits.
Just seems a right mess. Readings suggest cack handed TT. Cut out looks ready for PME and the coiled cable beneath reads as TNS! So a pick and mix.
I await the DNOs reply
 
I wasn't expecting the EC to be connected to the head, just sweated onto the lead. It sounds like whoever fitted the head left an airgap, for whatever reason.
 
The new cutout looks as if it is set up for pme but waiting for confirmation.

If it is 'set up for pme' the pme terminal will be exposed / accessible so do a loop test. If it isn't then do a two wire loop test on l & n or a 3 wire on l with both your n & e leads connected to the incoming n. The phase - neutral loop impedance figure WPD use for the existing network is 0.47 Ohms so equal or less than that value, it is quite possible they may have given you a pme connection. However do confirm before utilising.

As it is new, the job will have been recorded so any WPD employee with a laptop should be able to look up what was done, would take under a minute
 
As you may recall I have had some toing and froing with the WPD. Below is the conclusive email from the area manager no less. From what I see in your pictures there seems to be an obligation (legal) to maintain provide the PME earth that is obviously desparate to get out of the cut-out. Please use the below to remind them of their legal obligations and do feel free to quote from the below. I hope that is of use.
Dear Mr xxxxxxxxxxxxxx


Since our conversation about this topic I’m concerned that you may be somewhat anxious that the subject matter has been forgotten, this is not the case.


Indeed, a colleague within our policy team is currently working on an information/fact sheet that will be put onto our web site to obviate further related issues.


The concern you raised has been helpful in focusing light on the subject of both domestic and commercial earthing practices and will hopefully enable us to produce a helpful guide.


In advance of this “official” guide, I’m happy to confirm the following:


· ESQCR reg 24(4) and 24(5) refers to making an earth terminal available for new/replacement LV connection in all cases unless unsafe to do so.


· ESQCR reg 24(1) refers to maintaining equipment i.e. an earth terminal.


So Western Power Distribution should be observing the above two fundamental regulations.


Yours sincerely


Gwyn Jones

Distribution Manager, Bristol
 

Reply to Interesting cutout and apparent lack of earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
529
I am doing a new consumer unit install on a second story ex council flat. I’ve notice the mains come in in metal conduit with no CPC. On checking...
Replies
3
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
My customer has had a completely new supply installed to his garage. The DNO has not put a fuse in the cut out though. I'm guessing he needs to...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock